PowerChute cannot communicate with the Management Card

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PowerChute cannot communicate with the Management Card
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 PM . Last Modified: ‎2024-03-21 03:03 AM

0 Likes
10
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 PM . Last Modified: ‎2024-03-21 03:03 AM

PowerChute cannot communicate with the Management Card

I m try to conect to managment card and when i'm install Network Shutdown client on other computer. I see next message "Security information did not match information at 192.168.1.91". I can go on http protocol on managment card. What is it problem?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

ok, so it is what i expected. the only two issues that can cause this are you did not use the same administrator username for PCNS as what is used as the administrator username and password on your network management card (which appeared to be apc per your screenshot) or that authentication phrase in my screenshot is wrong.

did you use apc as the username when you installed PCNS? did you reset the authentication phrase on the NMC back to admin user phrase (case sensitive)? then you need to type it the same way when PCNS prompts for it.

if you did, i might reset the network management card to defaults, excluding TCP/IP. you could back up the config.ini file from it first which can be done via FTP. instructions on doing that are here if this device is on the public side of struxureware central or if it is on the private side, you'd need to connect to that private side and back it up via FTP. i am thinking a reset might be good if something is corrupt.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:13 PM . Last Modified: ‎2024-03-21 03:03 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:13 PM . Last Modified: ‎2024-03-21 03:03 AM

Hi

Sorted thank you. For some reason the authentication phrase was different on the powerchute to the NMC, even though it was a default install..?

Set them both back to defaults all fixed.

Thanks again

Message was edited by: grum13

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

Hi

What's NMC card firmware version? What user/password/authentication phrase did you type during PCNS install? Please note the administrator user name and authentication phrase authenticate the communication between PCNS and the NMC. Because of this you must set the values in PCNS to match the values for the NMC. (Note that it is allowable to set a password for PCNS that is different from the password for the NMC.)

In the NMC, the default administrator user name and password are both apc. The default setting for the authentication phrase is admin user phrase. If you input the correct user/password/auth phrase, the issue still occured, you may need to login to the card via web browser and navigate to UPS-PowerChute-Configuration(under PowerChute) to change auth phrase. After that, login off. Then install the PCNS again and type the user/auth phrase that same as those in the card. Hope it helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

Hi
I am currently having the same issue described in the original thread however, when I reset the credentials to be the same across the board, I'm still getting the mis-matched error. We have changed the password for log ins to the NMC but I triple checked to make sure I'm typing everything in correctly and everything should match up.
Any other tips?
Thank you.

Message was edited by: dgriffith@i3.com

Message was edited by: dgriffith@i3.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

Oh, sorry, yes I had. And I had installed and ran PC on another machine with the same settings/credentials.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:03 AM

how and where are you resetting the credentials? can you be more specific so we can ensure you got everything?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

Sure
I attached a screen shot. I'm logged into InfraStruxure Central, then logged into the UPS.

Message was edited by: dgriffith@i3.com

Message was edited by: dgriffith@i3.com

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

have you changed the powerchute authentication phrase? the screenshot you showed me is the username and password for the NMC itself.

Check under the NMC UPS tab and then look for powerchute configuration. you need to make sure the authentication phrase listed in that section is the same as it is when you install powerchute network shutdown. the default that you can set it to is admin user phrase

see my screenshot i attached.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

can you post a screenshot of the result you get? just want to ask around and have something to show and clarify. thanks.

the normal things that cause security mismatch are incorrect username between PCNS and NMC (username must match) and then the authentication phrase being incorrect that i showed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

Attached.

Thanks again.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:14 PM . Last Modified: ‎2024-03-21 03:02 AM

ok, so it is what i expected. the only two issues that can cause this are you did not use the same administrator username for PCNS as what is used as the administrator username and password on your network management card (which appeared to be apc per your screenshot) or that authentication phrase in my screenshot is wrong.

did you use apc as the username when you installed PCNS? did you reset the authentication phrase on the NMC back to admin user phrase (case sensitive)? then you need to type it the same way when PCNS prompts for it.

if you did, i might reset the network management card to defaults, excluding TCP/IP. you could back up the config.ini file from it first which can be done via FTP. instructions on doing that are here if this device is on the public side of struxureware central or if it is on the private side, you'd need to connect to that private side and back it up via FTP. i am thinking a reset might be good if something is corrupt.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore