Power Chute 3.0.2 have all options greyed out

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Power Chute 3.0.2 have all options greyed out
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All
Related Products
product field
Schneider Electric
PowerChute Personal Edition

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-28 10:26 AM

0 Likes
5
3122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 10:26 AM

Power Chute 3.0.2 have all options greyed out

First of all, hello to everyone here, honestly I am not used a lot to UPS and PowerChute but have been using the basics until now, the last check was less than a year ago

 

Then suddenly (as far as I remember), when I tried to use Power Chute every option appeared greyed out in the aplication running over Windows 10.

 

First if I open the program I see obviously almost every Option Tab greyed Out like this:

Image 0728_140745.png

 

Ok, then I connect any UPS and the program recognizes it BUT even if the Options in the Tab are now "Available", the Options within are still greyed out like this:

PowerChute1.PNGPowerChute2.PNG

 

I have no clue what the reason could be, searched for info since Monday and still can't figure it out, there are mention of specific options in some topics but not all of them like this

 

Can anyone please guide me on what to check? Could it be compatibility issue? Aplication Permissions? Any Option I am missing maybe? I will gladly add more info if needed but I am clueless on what to do. Thanks.

Labels
  • Labels:
  • GreyedOut
  • PowerChute
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-08-04 06:57 AM

In response to BillP
0 Likes
0
3030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-04 06:57 AM

First of all thanks a lot for the replys, honestly I wasn't able to find any relevant info before so I asked here and I am glad I got some answers.

 

For now I will wait until I get a new cord then, since it seems to be the cause of the issue and I hope it is because if not I have no clue 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 01:39 PM

0 Likes
4
3087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 01:39 PM

Hi,

 

The first issue was caused by the UPS not connected to the computer. The second issue appear the UPS is connected but PowerChute cannot determine the model. If you open PowerChute and go to the Technical Data page is the correct model and serial number displayed?

 
 

Technical Data Page.png

 

If it is not you should shutdown the computer and brain dead the UPS. See Schneider Electric FAQ FA158947 for assistance with the brain dead procedure. Once the UPS has been restarted, restart the computer. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-29 10:23 AM . Last Modified: ‎2021-07-29 12:34 PM

In response to BillP
0 Likes
0
3074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:23 AM . Last Modified: ‎2021-07-29 12:34 PM

Hello, first of all thanks a lot for the answer, you are my only hope at this point.

I checked what you asked but the UPS is recognized by PowerChute

 

Image 0729_160705.png

 

I took the screenshot and those ARE NO the Model and Serial of the 2 UPS I tried but as you can see PowerChute instantly recognize a UPS has been connected and the option panels turn on (still with the sub-options greyed out),

 

This happens with 3 different units so it doesn't seem like an UPS specific problem and more like a general problem with the software or some blocked option/permission but I have no idea what could it be.

 

What I am missing is doing a full uninstall, deletting all related folders and running Ccleaner to clean the registry, then installing all over again and see if something changes but a re-install already didn't solve the issue.

 

Any other thing to check? Thanks a lot for the guidance!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-03 11:24 AM

In response to BillP
0 Likes
2
3052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-03 11:24 AM

Could it be by change the USB-ETH cord not working properly or damaged? I don't have any other right now to test it but this one doesn't seem to be bruised anyway.

Also would it recognize a UPS connected, but not being able to fully receive the other data from it?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-08-04 06:29 AM

In response to Anonymous user
0 Likes
1
3042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-04 06:29 AM

@Anonymous user,

 

Yes to both questions. A damaged cable will cause communications issues.

 

When PowerChute is installed, it polls the UPS to determine the model and firmware. The model and firmware determine what features PowerChute will present. The screenshot shows PowerChute is receiving some data. However, it does not appear to be receiving all data points. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-04 06:57 AM

In response to BillP
0 Likes
0
3031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-04 06:57 AM

First of all thanks a lot for the replys, honestly I wasn't able to find any relevant info before so I asked here and I am glad I got some answers.

 

For now I will wait until I get a new cord then, since it seems to be the cause of the issue and I hope it is because if not I have no clue 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore