Possible Bizarre APC Back-UPS Pro 650 Behavior

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Possible Bizarre APC Back-UPS Pro 650 Behavior
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
4
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Possible Bizarre APC Back-UPS Pro 650 Behavior

Do I have a problem with my Pro 650?

Connected to the pro battery backup side are my PC, a flat screen monitor, cable modem, router, etc; connected to the filter side are my Lexmark Optra R+ laser printer.

This configuration, unperturbed, but for a UPS battery replacement 2 years ago, has been working for a long time, the UPS "clicking" when the printer switches on or draws power, such as during a printer thermal head heat cycle.

Suddenly, yesterday, after having had the PC on for several hours, I switched the printer on, and my PC shut down instantly. Problem repeatable, but not every time. Disconnected the printer data line, no change. Moved the printer off the ups to another socket on the same AC outlet, no change. Swapped the printer for an identical printer. No change. Switched on printer, booted PC, worked for a few minutes, then bam, the PC shut down hard.

Can some filter electronics have failed in the Pro 650 that allows surges, say when the thermal mechanism of the printer switches on, back upline into the UPS side and thus into the PC, which then senses the surge and shuts down?

By swapping printers, I believe I have eliminated the printer as a potential problem source. I can't think how the PC could be at fault - i.e., a partial power supply failure introducing extreme surge sensitivity. That leaves the UPS, but the failure mode of having the printer not connected to the UPS but both merely connected to the same AC wall socket, has me stumped.

Help!

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • shutdown
  • Unexpected
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Gary,

You may also trade in your old unit to a new unit. Click on the below link to know more information about trade UPS program.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=298

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Gary,

I suspect that the UPS transfers to battery mode whenever the printer in question starts/draws power. I think that the UPS is not able to provide power on battery mode. Connect a non critical equipment to the UPS battery backup outlet and stimulate a power failure by unplugging the UPS from the wall, and check if it powers the equipment on battery mode. If it does not support on battery mode, you may need to replace the battery. However, please verify the front lights indication before replacing the battery. The UPS performs a self test to check the battery integrity at start up and every 14 days automatically. What lights are on the front of the UPS after you switch on the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

One thing that comes to my mind when you mentioned about having a laser printer in your configuration is that due to the age of your UPS some mechanism of the unit might be failing. Whenever you start up your UPS or it heats up the thermal mechanism it draws a lot of current to do it and it is what do we call as inrush current. Certain UPS is sized incorrectly can go on an Overload condition which would then turn off the outlets on the UPS.

Listed below are some knowledge base articles that might help you learn more about Back-UPS.
- [Recommendations for protecting a laser printer|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=23&p_created=1000309963&p_s...]
- [Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=20&p_created=1000309963&p_s...]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Thank you for the suggestions. As I was reading your response, the two weeks must have ticked over, because the "bad battery" symbol began to audibly alarm and the X symbol indicator lght on the UPS came on. I would never have dreamed that the self-test interval was two weeks - two days max seems much more prudent.

As this would have been the second replacement battery, I plan to junk the UPS and buy a new one.

Thanis, again, for your ideas & recommendations.

Gary

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Gary,

You may also trade in your old unit to a new unit. Click on the below link to know more information about trade UPS program.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=298

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of