New infrastruxture

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New infrastruxture
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
2
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

New infrastruxture

Hi Gents,

I'm a new user in your forum,
We're currently using a traditional dual 30KvA UPSs that having a problem (internally and with the stationary batteries).
I fought to introduce the new Symmetra PX 40, our current load is 20KvA, and we are planning to add new Blade and SAN enclosures.
We have a large generator with ATS ready. The local APC dealer here offered us with symmetra PX 40 N+1 scalable to 80 with 40 battery units.
My concerns are:
- Is the UPS capacity will be enough for our current and coming expansion?
- Is there any potential failure on the new UPS (when output power disappears) because this is our biggest nightmare?!
- What is the heat capacity (BTU) of the UPS (for cooling purpose)?

APCFAN
Regards

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • apc
  • cooling
  • data_centers
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Hi APCFAN,


1) Is the UPS capacity will be enough for our current and coming expansion?
- You mention have dual 30KVA UPS, do you mean you have 2 30KVA UPS? Its hard to say if a 40KW will be enough or if you will need the 80KW Symmetra PX. There is also the new PX2 which can go all the way up to 500KW. It really will depend on the actual power draw you are expanding too. You may want to take into account expansion over the next 5+ years as well. If you go with a frame for a PX or PX2 that can handle much more than your current load you can always start off with only a few power modules and then add them as your power needs grow.

2) Is there any potential failure on the new UPS (when output power disappears) because this is our biggest nightmare?!
- This is assuming you will have a redundant power module. Each power module is an individual unit (10KW) and can be removed for repair without disruption to the load. These units also have built in static switches that provide a safe means of transferring the load off of the ups without interruption during critical repairs and maintenance.

3) What is the heat capacity (BTU) of the UPS (for cooling purpose)?
- 11884.00 BTU/hr full load of 40kva/kw and 22744.00 BTU/hr full load of 80kva/kw.

I hope this answered your questions. If you want to pursue this course I would strongly urge you to contact APC sales and they can help size everything up and give you the cost of different solutions so you can compare them.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Hi Gents,

I'm a new user in your forum,
We're currently using a traditional dual 30KvA UPSs that having a problem (internally and with the stationary batteries).
I fought to introduce the new Symmetra PX 40, our current load is 20KvA, and we are planning to add new Blade and SAN enclosures.
We have a large generator with ATS ready. The local APC dealer here offered us with symmetra PX 40 N+1 scalable to 80 with 40 battery units.
My concerns are:
- Is the UPS capacity will be enough for our current and coming expansion?
- Is there any potential failure on the new UPS (when output power disappears) because this is our biggest nightmare?!
- What is the heat capacity (BTU) of the UPS (for cooling purpose)?

APCFAN
Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

0 Likes
0
1115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:04 PM . Last Modified: ‎2024-03-21 01:08 AM

Hi APCFAN,


1) Is the UPS capacity will be enough for our current and coming expansion?
- You mention have dual 30KVA UPS, do you mean you have 2 30KVA UPS? Its hard to say if a 40KW will be enough or if you will need the 80KW Symmetra PX. There is also the new PX2 which can go all the way up to 500KW. It really will depend on the actual power draw you are expanding too. You may want to take into account expansion over the next 5+ years as well. If you go with a frame for a PX or PX2 that can handle much more than your current load you can always start off with only a few power modules and then add them as your power needs grow.

2) Is there any potential failure on the new UPS (when output power disappears) because this is our biggest nightmare?!
- This is assuming you will have a redundant power module. Each power module is an individual unit (10KW) and can be removed for repair without disruption to the load. These units also have built in static switches that provide a safe means of transferring the load off of the ups without interruption during critical repairs and maintenance.

3) What is the heat capacity (BTU) of the UPS (for cooling purpose)?
- 11884.00 BTU/hr full load of 40kva/kw and 22744.00 BTU/hr full load of 80kva/kw.

I hope this answered your questions. If you want to pursue this course I would strongly urge you to contact APC sales and they can help size everything up and give you the cost of different solutions so you can compare them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore