PC not powering back up when power restored

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PC not powering back up when power restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

0 Likes
4
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

PC not powering back up when power restored

I bought a new Backup ES 725 to manage my PC, 19" lcd monitor and small network switch. Runs fine, switches to battery fine and hibernates windows. My problem is that the computer is not powering back on when AC is restored. Bios is set to power on on AC loss and it works just fine when I test it manually.

For the the UPS, I do see it killing power for about 1 second (via leds on network switch) but it doesn't seem to be long enough for the PC to notice the loss. Is there a way to increase the delay the UPS kills the power or some other suggestions to get around this issue.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • reboot
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

I bought a new Backup ES 725 to manage my PC, 19" lcd monitor and small network switch. Runs fine, switches to battery fine and hibernates windows. My problem is that the computer is not powering back on when AC is restored. Bios is set to power on on AC loss and it works just fine when I test it manually.

For the the UPS, I do see it killing power for about 1 second (via leds on network switch) but it doesn't seem to be long enough for the PC to notice the loss. Is there a way to increase the delay the UPS kills the power or some other suggestions to get around this issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

Just the length of the power loss.

I do actually see the power being cut when ac service is back on, it clicks and everything. It appears in my case that the time it kills the power just isn't long enough for my power supply/computer to drain enough charge to notice the power loss. Any other suggestions as a work around (without getting a more expensive ups)? Otherwise I'll have to leave the usb out and use it unmanaged since I have to have it on when possible. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

-

Message was edited by: KVAr, incorrect response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

He is talking about the automatic graceful shutdown capabilities of the UPS. After a shutdown is initiated, there is an OS shutdown delay (not configurable in a Back-UPS). Once this delay has expired, the UPS goes into a sleep mode where it will cut power to the on battery outlets. The idea behind this is that once normal AC power returns, the UPS will wake up, resupply power to the outlets, and a computer system could be configured to automatically boot when it sees its power source return.

The momentary power cut he is referring to happens if normal AC power returns after a graceful shutdown has begun, but before the UPS goes to sleep. In this case, the UPS will still complete its shutdown delay, and as soon as it goes to sleep (and cuts power), it will wake up. A computer should see this as a power cycle, and theoretically boot back up automatically. Non of this hurts the computer, because at this time, the OS has already been brought to a shutdown state.


catfish,
Could you try your test again, but do not restore power to the UPS until after your UPS goes into its sleep mode? You should be able to tell when its 'sleeping' because it will stop outputting battery power. Plugging a lamp into the battery outlets should be an easy way to know for sure.

Once its sleeping, give it a few seconds, and then plug the UPS back into AC power. This should have been plenty of time for your computer to recognize that power had been cut, and has returned. Once the Power is back to the UPS, the lamp should come on automatically, and hopefully your computer too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

0 Likes
0
1492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:37 PM . Last Modified: ‎2024-03-26 02:14 AM

I bought a new Backup ES 725 to manage my PC, 19" lcd monitor and small network switch. Runs fine, switches to battery fine and hibernates windows. My problem is that the computer is not powering back on when AC is restored. Bios is set to power on on AC loss and it works just fine when I test it manually.

For the the UPS, I do see it killing power for about 1 second (via leds on network switch) but it doesn't seem to be long enough for the PC to notice the loss. Is there a way to increase the delay the UPS kills the power or some other suggestions to get around this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore