Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PC Reboots When Switching to UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PC Reboots When Switching to UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
7
2575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

PC Reboots When Switching to UPS

Hello,
I have just built a new PC. Gigabyte EP35-DS3R, E6600, Antec Earthwatts 500 PS, XP Pro SP3. I have a Back-UPS 650 (BE650BB). I am running Powerchute personal 2. As stated in the title, if I pull the UPS plug from the wall outlet, or there is a power outage, rather than switching to UPS power immediately, the PC reboots then runs on UPS power. The UPS has been working fine on the PC I just replaced (Asus A8N-E Opteron 175, Antec TruePower 2 480 PS). The new system draws much less power. I have contacted APC, Antec, and Gigabyte and no-one has any answers. It does not matter if I am booted into the OS or sitting with the BIOS screen displayed, when I pull the plug the PC reboots. The battery is 100% charged and has been regularly passing self tests.
Please Help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

Problem solved. I purchased a cheap store brand at Circuit City. The brand is Nexxtech. Made in China. 3 year warranty. 1000 VA 600 W. It states on the box that the typical transfer time is 4ms.
It also states that it uses a simulated sine wave. Apparently the transfer time was my issue. $109.00 US. Probably can be had elswhere for cheaper.
So, APC won't be getting $300.00 or more dollars from me for a SmartUPS. Thanks to all who tried to help, and I hope this info will prove useful to others.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

Thank you all for helping. That last link is definitely very helpful. Does it mean that I don't worry about the "up to 8ms switching time" and getting a larger unit should solve my problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

That's good to know cos I was telling people who were having the same issue to exchange their UPS for higher VA ones, but it seems this is not the only issue.

Is there a way to produce more affordable pure sine wave units or at least smaller ones, like 500 to 600VA? In my country the smart ups units are ridiculously expensive. With Active PFC PSUs becoming a common thing, pure sine wave UPSses should become cheapper or less "fancy" units for the residential market should be made, I think.

Thank god I don't have any issue on a Zalman 460watt. At least not yet! Apart from the buzzing noise coming out of it while on battery, it works well with the 8ms typical transfer time on a 600VA Backup ES unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
EZ_Button_apc
Contributor

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

Sounds like your system is sensitive to the transfer time of the UPS. A back-ups will have a 4-8 second transfer time to battery. It's generally not a problem for power supplies, but you never know. I'd try getting in touch with your power supply manufacturer and finding out if it can handle momentary power drops of a few milliseconds. APC makes other UPS's with less or no transfer time to battery (Smart-UPS and Smart-UPS RT), but unfortunately, they are more expensive.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

I believe you meant 4 to 8ms, not seconds!

I think this might be helpful:

http://emea-en.apc.com/cgi-bin/emea_en.cfg/php/enduser/std_adp.php?p_faqid=8883&p_created=1193079387...

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Cap1_apc
Contributor

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

I think your best bet would be the Smart-UPS line for a PFC power supply. I've personally seen cases where not only does the PS overload the unit, but also ones where the 8 millisecond transfer actually drops the load. The overload scenario is more likely, but I would see if your PS manufacturer can elaborate on the lag time the PS can sustain.

The Smart-UPS line essentially takes care of both of these issues:
- It transfers in 2-4ms
- It can sustain a brief overload much better than the Back-UPS line

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

So I went out and bought a BX1300LCD which is 780 watts. Same issue exists. Maybe the Smart Series is the only solution.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

0 Likes
0
2576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:24 PM . Last Modified: ‎2024-03-26 12:29 AM

Problem solved. I purchased a cheap store brand at Circuit City. The brand is Nexxtech. Made in China. 3 year warranty. 1000 VA 600 W. It states on the box that the typical transfer time is 4ms.
It also states that it uses a simulated sine wave. Apparently the transfer time was my issue. $109.00 US. Probably can be had elswhere for cheaper.
So, APC won't be getting $300.00 or more dollars from me for a SmartUPS. Thanks to all who tried to help, and I hope this info will prove useful to others.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore