P1-GR; HIGH VOLTAGE PROBLEM
  • P1-GR; HIGH VOLTAGE PROBLEM
2151
123
Posted: ‎2021-06-28 02:14 AM . Last Modified: ‎2024-03-27 02:29 AM
755
Hi All,
This product is working on 270Volts, and does not close the current on load. ( 7-8 Ampers) And what is the working parameters for this unit, by ampers and by volts?
I asked our EMEA region support team for some feedback. Here is what I received specific to this model:
I think you are asking why this device doesn't break the line while 7-8 amps is flowing through - in general there is no circuit breaker inside this model, it relies on wall socket protection (which is usually higher rate, 7 amps wouldn't trip wall 16 or 20 amps breaker anyway). This device utilizes MOV surge protection but no over-current protection. Also, if you needs to limit voltage to your load, this cannot be done by surge protector and you would need either Line-R voltage regulator or UPS.