Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

No loads connected, yet 3, 4, & 5 are lit ??

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: No loads connected, yet 3, 4, & 5 are lit ??
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
PeteCress_apc
Ensign PeteCress_apc
Ensign

Posted: ‎2021-06-29 10:51 PM

0 Likes
3
328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:51 PM

No loads connected, yet 3, 4, & 5 are lit ??

This was originally posted on APC forums on 12/4/2012


This is my second UTS6H.

First one, APC support decided was faulty after the electrician put in several manhours and lots of my cell phone minutes trying to make it work.

So I'm running scared... -)

The electrician comes back for another try on Thursday and I figured I'd hang the switch on the wall, plug some power in to the UPS receptacle, and step through the initial setup before he gets here.

Initial setup went smoothly - or, at least, it didn't throw any errors or act unexpectedly.

But now I note that with nothing connected, I've got lights 3, 4, and 5 lit.

viz: http://tinyurl.com/bpgelx6

This doesn't jell for me. Seems like with nothing connected, I should see either all or no lights.

OTOH, it seems like the chances of getting two defective units in a row is vanishingly low.

Having said that... If the light situation indicates something obviously wrong, I want to call off the electrician before he puts any more billable hours into this job.

Can anybody comment?

Edit 2012 12-06 09:55
For anybody else with this issue, I finally managed to get through APC's (horrendous....) voice menu system and talk to a support guy.

He said that this would be a normal condition.



Edit 2012 12-06 12:21
What the support guy left out was that if all lights are not lit, there will probably be a problem once the box is tested.

Further investigation revealed that the power source for some circuits were defaulted to other than "Gen". I'm not sure what bc the label was truncated by the display.

Making all circuits' power source = "Gen" caused all lights to come on as expected and the box perform as expected under both utility and generator power.
.
.
.
.
.
.
.
.
.

Message was edited by: PeteCress

Message was edited by: PeteCress

Labels
  • Labels:
  • Universal Transfer Switch
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:52 PM

0 Likes
0
328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:52 PM

This reply was originally posted by Dana on APC forums on 12/22/2012


I have found this unit is not documented well. I posted an anomaly you might want to read about the wizard setup. The behavour you are talking about I think I might have even run into. What was the problem with your first unit?

Message was edited by: Dupre29

See Answer In Context

Reply
Replies 3
PeteCress_apc
Ensign PeteCress_apc
Ensign

Posted: ‎2021-06-29 10:51 PM

0 Likes
0
328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:51 PM

This was originally posted on APC forums on 12/4/2012


This is my second UTS6H.

First one, APC support decided was faulty after the electrician put in several manhours and lots of my cell phone minutes trying to make it work.

So I'm running scared... -)

The electrician comes back for another try on Thursday and I figured I'd hang the switch on the wall, plug some power in to the UPS receptacle, and step through the initial setup before he gets here.

Initial setup went smoothly - or, at least, it didn't throw any errors or act unexpectedly.

But now I note that with nothing connected, I've got lights 3, 4, and 5 lit.

viz: http://tinyurl.com/bpgelx6

This doesn't jell for me. Seems like with nothing connected, I should see either all or no lights.

OTOH, it seems like the chances of getting two defective units in a row is vanishingly low.

Having said that... If the light situation indicates something obviously wrong, I want to call off the electrician before he puts any more billable hours into this job.

Can anybody comment?

Edit 2012 12-06 09:55
For anybody else with this issue, I finally managed to get through APC's (horrendous....) voice menu system and talk to a support guy.

He said that this would be a normal condition.



Edit 2012 12-06 12:21
What the support guy left out was that if all lights are not lit, there will probably be a problem once the box is tested.

Further investigation revealed that the power source for some circuits were defaulted to other than "Gen". I'm not sure what bc the label was truncated by the display.

Making all circuits' power source = "Gen" caused all lights to come on as expected and the box perform as expected under both utility and generator power.
.
.
.
.
.
.
.
.
.

Message was edited by: PeteCress

Message was edited by: PeteCress

Reply
PeteCress_apc
Ensign PeteCress_apc
Ensign

Posted: ‎2021-06-29 10:52 PM

0 Likes
0
328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:52 PM

This was originally posted on APC forums on 9/22/2013


> What was the problem with your first unit?

Sorry to be so long in responding - can't figure out how to get email notifications on this board.

Problem with original remains unknown.   Schneider RMA'd it and sent us another one at the same time - so Schneider gets five stars for doing the right thing . but the actual problem remains unknown.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:52 PM

0 Likes
0
329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:52 PM

This reply was originally posted by Dana on APC forums on 12/22/2012


I have found this unit is not documented well. I posted an anomaly you might want to read about the wizard setup. The behavour you are talking about I think I might have even run into. What was the problem with your first unit?

Message was edited by: Dupre29

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc