New purchase BE750G battery backup; Battery manufacture date says October 2014???

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New purchase BE750G battery backup; Battery manufacture date says October 2014???
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:03 AM

0 Likes
4
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:03 AM

New purchase BE750G battery backup; Battery manufacture date says October 2014???

I bought a new APC battery backup tonight. The model is BE750G, and the specs say 750va / 450 watts. When I opened the box there was a slip taped to the unit, and it says that the manufacture date was October 2014. I'm not very happy about that. Based on what I'm reading about the discharge rates of stored batteries, and other forum posts here in this forum, I guess I'm wondering if I should just return it for refund. The battery sat in storage condition awaiting sale for 26 months. Would I be foolish to keep it?

I want to ask about APC's warranty on this battery/unit. I have 14 days to return this unit, but after that the store says I would have to contact APC regarding warranty. If something were to happen 15 days from now, would APC require that I spend my money to ship the unit or battery back to them? I just don't want to have to pay for that, seeing how I bought this tonight and it was rather expensive. Since I wasn't shopping online, I didn't get an especially good deal.

Convince me to keep it or return it please. If a bad battery means I would have to pay to ship it or the whole unit back to APC, I think I'm going to return it unless APC wants to send me a new battery right now. Is that something that APC would do?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • be750g
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

So, I waited almost 24 hours before performing the test. Battery as fully charged as it was going to get. I plugged in 3 lamps, with a total of 5 light bulbs. Total wattage of all bulbs is 209 watts. Pulled the plug and the power went out after about 8.5 minutes. According to what I'm seeing online in regards to runtime charts and tests for this model, I should have got more like 12 to 13 minutes.

I'll call APC on Monday. If they want to send a new battery at their expense, then I don't mind keeping the unit, but if they won't I'll just return it.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:03 AM

0 Likes
0
1330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:03 AM

I would be quite surprised if this unit came from a major retailer.

I think it'd be worth hooking up the battery, plugging it in and doing a test with a dummy load (a bunch of incandescent light bulbs would work well for this, running to about 50% of the unit's capacity). Let the unit charge for at least eight hours before you do this. If it passes the test, by which I mean it carries that 50% load for at least 15 minutes or so, I'd have no problem at all using it.

I'd give it about 75-80% odds of being just fine and giving you many years of reliable service before the battery would need to be replaced. Electronically it's every bit as good as a new one.

I'm not sure what APC would say about warranty coverage on this unit. There'd be no harm in calling to ask.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
1330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

I bought it at Batteries + Bulbs. I'm not sure what classifies a "major retailer", but batteries is their business, so I thought it would be safe to buy from them.

I'll do your dummy test and see what happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
1330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

On 12/24/2016 12:34 AM, Robert said:

I bought it at Batteries + Bulbs. I'm not sure what classifies a "major retailer", but batteries is their business, so I thought it would be safe to buy from them.

Color me quite surprised in that case. surprised By "major retailer" I mean any retail business with a multi-state, if not nationwide or even worldwide retail presence. Batteries + Bulbs certainly ought to qualify in at least one of those categories.

Still, I had no idea they sold complete and new uninterruptible power supply products there. Perhaps a lot of other people are similarly unaware, and maybe that would explain the "new old stock" unit you got.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
1330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-27 01:02 AM

So, I waited almost 24 hours before performing the test. Battery as fully charged as it was going to get. I plugged in 3 lamps, with a total of 5 light bulbs. Total wattage of all bulbs is 209 watts. Pulled the plug and the power went out after about 8.5 minutes. According to what I'm seeing online in regards to runtime charts and tests for this model, I should have got more like 12 to 13 minutes.

I'll call APC on Monday. If they want to send a new battery at their expense, then I don't mind keeping the unit, but if they won't I'll just return it.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore