Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Needin advise on custumized second hand UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Needin advise on custumized second hand UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:50 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
5
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:50 PM . Last Modified: ‎2024-03-26 12:57 AM

Needin advise on custumized second hand UPS

Hello every one. I recently bought a " Back-UPS ES 650" with it was a modifyed Smart-UPS XL 24V Battery Pack rewired to put out 12V. this was wired to run the UPS, the cabal was fairly professional quality.
My question is.
Would this setup be likely to damage the the UPS I bought. It is working as is now.
Thanks for any advice.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

Is it able to charge up to and maintain 13.6-13.8v? If not, the battery may not last as long as it could.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:50 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:50 PM . Last Modified: ‎2024-03-26 12:57 AM

Upon reading the fist reply, I wounder if putting an inteligent batt charger/maintainer on the batt pack would help protect the chargin circuit. Or would that damage the UPS?
There is no Warrenty on the unit. I jsut usin it on an offsite as a back up fer generator so there no Electrical codes to worry about.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Cap1_apc
Contributor

Posted: ‎2021-06-28 08:50 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:50 PM . Last Modified: ‎2024-03-26 12:57 AM

Hello,

Although doing this is completely unsupported by APC and most likely voids your warranty, it could potentially "work" but perhaps not up to the performance you are looking for.

Several things to keep in mind:
- Because the UPS does a runtime/time calculation during self tests, and is expecting a much smaller battery in amp hours, runtime calculations could be off.
- For the same reason, the replace battery indicator may not/ will not function correctly. My personal advice is to check the battery manually every 3-6 months
- The recharge of the much larger battery string will put stain on the charging circuit (in this unit, the charger is only rated at 7W). Depending on the total amp/hour of the battery string, it could take the charger days to get back up to 100%. If I were to guess, this is where you might see a hardware failure.
- By doing this you void APC warranty, possible electric codes, and equipment protection policies etc, etc.

With all of this in mind, and in my professional opinion, if you are looking for extra runtime your safest bet is to either purchase the correct smart-ups to support the battery pack you have, or get a whole new UPS that supports an external battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Cap1_apc
Contributor

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

I would imagine that would take some of the strain off the internal charger. But again, it sounds like that this setup is turning into a pretty expensive "unsupported" option. You might want to weigh in the cost of getting this to work (maybe) vs. a new UPS sized appropriately. Of course this is completely up to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

Well fountenetly the UPS and batt was only $50, and I have a batt charger already. I can't afford a new one, tis why I hoped this would work. Thanks fer yer help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

Is it able to charge up to and maintain 13.6-13.8v? If not, the battery may not last as long as it could.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore