Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Need Battery Constant reset value for Back Ups Pro 1000 (BP1000)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Need Battery Constant reset value for Back Ups Pro 1000 (BP1000)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

0 Likes
3
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

Need Battery Constant reset value for Back Ups Pro 1000 (BP1000)

I installed new batteries and need to reset the battery constant value for three USA model BP1000 Back UPS Pro 1000's (firmware version 13.J.D):

http://www.apc.com/resource/images/products/200/bp1000_f_v_200x100.jpg

I already spent the money on the new batteries and also on the smart signalling cable needed for this.

The hyperterminal procedure described here works: http://www.rm.com/support/technicalarticle.asp?cref=tec817072

I found a table of battery constant values here: http://apcupsd.com/manual/manual.html#resetting-the-ups-battery-constant

But, the BP1000 is not on this list.

So, I e-mailed support for the answer. Firstly they asked "what I was referring to." I replied:

Quote:

I can confirm that the hyperterminal procedure above works exactly as described for an older Back-UPS Pro BP1000. My current battery constant is at NA. I need to know the value to reset it to, after putting in a new RBC6 battery.

This is their response:

Quote:

Please note BP1000 is a discontinued model and it does not the option to reset battery constant table. I just wanted to make sure before answering. If you have any other concern, please let me know.

Well, yes, actually, I do have another concern. I explained that the hyperterminal procedure works. So, in fact, it does "option to reset the battery constant table."

I know this is my first post, but, APC is a pretty big company, and my jaw is pretty much on the floor. I think this is a first for me, where, officially, I have been blatantly lied to, officially by support. And, for such a simple problem... it has an extremely short, and very direct answer! Which they refused to give me! So, I am quite a bit upset, especially after spending money directly with APC!

I am posting with the hope, that somebody knows it.

Please?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery_constant
  • bp1000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

Yes, I understand on the support response. I agree it was lacking explanation and certainly could've been much better. I will look up the chat correspondence and address the specific incident internally.

On these models, I guess you'd be limited to a runtime calibration if the reported runtime is not accurate. Let me know if you need help with that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

Hello,

I don't personally think support intentionally/officially gave you the incorrect answer as this is typically a procedure that is done only on Smart-UPS. In the early days of these UPS systems, Back UPS and Smart UPS shared some of the same hardware/firmware platforms but today they are completely separate. We do not receive requests on these older models and battery constants often at all so if anything, I can only fault support (in my mind) for maybe not double checking with someone else who has more experience.

Putting that aside, NA refers to Not Applicable for any response when talking to UPSs of these type. Just because you can get in via HyperTerminal or serial does not mean it supports every single feature/value the Smart UPS product family does.'NA' is not a valid value as a constant. I double checked my list of battery constants and I do not have it on my list unfortunately. If I had it, I would provide it to you for use at your own risk of the procedure you found since Smart UPS engineering I know did not want to have customers to this anymore since some customers have damaged their UPS by entering in the wrong commands previously and blamed us. To add to that, we don't have this procedure on our own website though for this reason.

If you want to try and change it at your own risk, I would assume SU1000 is similar as on my list, I have BP420SI/SU420iNET listed and the constant is A0. That is also on the chart on the apcupsd website I noticed. But, I don't think you'll be able to change it since you're receiving NA for Not Applicable for this UPS model. Otherwise, perhaps you received NA because you hit an incorrect key or the timing on accessing the key combination for the constant was incorrect.

Let me know if you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

I hit + and - and confirmed that I was able to change the constant to different values. I don't remember what any of them were, but it didn't occur to me until you mentioned that "NA" means "Not Applicable" that N is not a hexadecimal digit.

I left it at NA (I didn't want to change anything until I got a definite answer), but if "NA" really means "Not Applicable" then perhaps changing it to something else would be bad.

I will check the other two BP1000's in Hyper Terminal and confirm that they also have constants of NA, as one of them has never been used. In fact, if one of them has never been used, then whatever the constant setting that has would be the answer. But, while it hasn't been "used" as in plugged in, the yellow connector is attached at the back, so it did have the batteries connected. Obviously it needs new batteries, but, since the batteries were connected, it's possible the constant changed to something else. But, if "NA" = "Not Applicable", then I guess all of that is moot.

I apologize for saying support "lied," I felt justified in saying that, given the information I had. Really, all they would have had to say is something like, "BP1000 is a discontinued model and it does not the option to reset battery constant table, as a value of "NA" is not a valid hexadecimal setting and stands for 'Not Applicable.'"


It's not like I'm a complete cheapskate and refuse to buy new equipment, I just felt like these older models still work and rather than throw them away I could put them to use. tongue-out

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:46 PM . Last Modified: ‎2024-03-20 03:52 AM

Yes, I understand on the support response. I agree it was lacking explanation and certainly could've been much better. I will look up the chat correspondence and address the specific incident internally.

On these models, I guess you'd be limited to a runtime calibration if the reported runtime is not accurate. Let me know if you need help with that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of