Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84520members
353751posts

Matrix 5000 replace battery pack

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
ckh0d0a_apc
Crewman
Crewman
0 Likes
3
158

Matrix 5000 replace battery pack

This was originally posted on APC forums on 1/12/2010


We have a replacement battery pack for the failed pack. There are 4 of these battery packs interconnected. The user manual says I can swap the battery pack while the system continues to run.

AND - the pack to be replaced is easily accessible. When things appear too easy, I worry that I've overlooked something. But right now I should be able to hot swap the battery packs, taking care to replace cables and wires in the exact pattern as they are removed.

So - is it true I can merely disconnect one battery and swap with the good one? Hate to drop our servers today.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
158

Re: Matrix 5000 replace battery pack

This reply was originally posted by Laurie on APC forums on 3/3/2010


To add on what Nix said, you would have to replace an entire Smartcell battery pack, but not the whole Smartcell-XR battery pack. The latter has the user replaceable batteries but the former does not. Basically, even if you try to replace the battery inside a little Smartcell, the replace battery light will stay on because all of the circuitry inside thinks it's still an original battery.

But yes, they're all hot swappable too.

See Answer In Context

3 Replies 3
ckh0d0a_apc
Crewman
Crewman
0 Likes
0
158

Matrix 5000 replace battery pack

This was originally posted on APC forums on 1/12/2010


We have a replacement battery pack for the failed pack. There are 4 of these battery packs interconnected. The user manual says I can swap the battery pack while the system continues to run.

AND - the pack to be replaced is easily accessible. When things appear too easy, I worry that I've overlooked something. But right now I should be able to hot swap the battery packs, taking care to replace cables and wires in the exact pattern as they are removed.

So - is it true I can merely disconnect one battery and swap with the good one? Hate to drop our servers today.

BillP
Administrator Administrator
Administrator
0 Likes
0
158

Re: Matrix 5000 replace battery pack

This reply was originally posted by Jan on APC forums on 3/3/2010


There is no need to swap the Smartcell-XR entirely since the RBC14 Battery pack is still available.
However, that frame would need to be disconnected during the replacement.

BillP
Administrator Administrator
Administrator
0 Likes
0
159

Re: Matrix 5000 replace battery pack

This reply was originally posted by Laurie on APC forums on 3/3/2010


To add on what Nix said, you would have to replace an entire Smartcell battery pack, but not the whole Smartcell-XR battery pack. The latter has the user replaceable batteries but the former does not. Basically, even if you try to replace the battery inside a little Smartcell, the replace battery light will stay on because all of the circuitry inside thinks it's still an original battery.

But yes, they're all hot swappable too.