LONGER RUN TIME / Upgrading Battery / Using a Bigger Battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • LONGER RUN TIME / Upgrading Battery / Using a Bigger Battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

0 Likes
3
2595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

LONGER RUN TIME / Upgrading Battery / Using a Bigger Battery

Hi, I have a Back-UPS CS 350 and I'm looking to replace the battery. By default it comes with a 12v 7Ah battery, but I want to put a larger capacity battery inside. I've been looking at a 18Ah or 21Ah. My apologies if this has already been discussed, I searched the forums and couldn't find anything..

Now, of course, I know this is not recommended by APC/voids warranty etc etc. And of course, that the battery won't fit in the box. This is as much an experiment as it is a solution. I just want to know of any 'side effects' or problems I may have by doing this, or anyone else's experience with doing something like this. I received this unit for free with a dead battery, so I don't really care if I break it. I'm a technician and I know my way around electronics.

I have heard that using a larger capacity, which leads to longer discharge time, can cause the unit to become hotter. I was going to install a fan in the unit to help keep it cool. And another thing I've heard is that, while using a larger battery, the unit will discharge normally (just last longer), but the charging circuit will not be able to completely charge the larger battery.. But everyone just says it 'might'. Has anyone done or tried this, and was it able to charge correctly?

Thanks! Any information or suggestions is appreciated!

Gregory

Message was edited by: KnightRacer1K

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 12v_21ah
  • bigger_battery
  • higher_capacity
  • last_longer
  • replace_battery
  • upgrade_battery
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

0 Likes
0
2595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

No one has ever put a bigger battery in one of these UPS's?

Ok, how about this, what If I buy two or three 12v 7Ah batteries, and connect them in parallel? Would that be more efficient, as far as the charging circuit? Or would it essentially be the same as buying one larger 12v 21Ah battery?

Thanks! Any, any input or feedback is much appreciated!

-Gregory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

0 Likes
0
2595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

keep in mind that these UPSs, especially the smaller ones are designed to charge the batteries that they ship with in 18 hours or so. they have small chargers like between 10-30 watts. using a third party larger battery makes sense for a really long time but you essentially void your warranty and then will run into longer charge times.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

0 Likes
0
2596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

No one has ever put a bigger battery in one of these UPS's?

Ok, how about this, what If I buy two or three 12v 7Ah batteries, and connect them in parallel? Would that be more efficient, as far as the charging circuit? Or would it essentially be the same as buying one larger 12v 21Ah battery?

Thanks! Any, any input or feedback is much appreciated!

-Gregory

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

0 Likes
0
2594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:19 AM . Last Modified: ‎2024-03-22 12:53 AM

Hi, I have a Back-UPS CS 350 and I'm looking to replace the battery. By default it comes with a 12v 7Ah battery, but I want to put a larger capacity battery inside. I've been looking at a 18Ah or 21Ah. My apologies if this has already been discussed, I searched the forums and couldn't find anything..

Now, of course, I know this is not recommended by APC/voids warranty etc etc. And of course, that the battery won't fit in the box. This is as much an experiment as it is a solution. I just want to know of any 'side effects' or problems I may have by doing this, or anyone else's experience with doing something like this. I received this unit for free with a dead battery, so I don't really care if I break it. I'm a technician and I know my way around electronics.

I have heard that using a larger capacity, which leads to longer discharge time, can cause the unit to become hotter. I was going to install a fan in the unit to help keep it cool. And another thing I've heard is that, while using a larger battery, the unit will discharge normally (just last longer), but the charging circuit will not be able to completely charge the larger battery.. But everyone just says it 'might'. Has anyone done or tried this, and was it able to charge correctly?

Thanks! Any information or suggestions is appreciated!

Gregory

Message was edited by: KnightRacer1K

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore