APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-06 01:10 AM
My UPS does not seem to function properly, the event log states the following continuously, every day, every few minutes:
6/5/24 22:09:29 Battery Charge in Range
6/5/24 21:44:15 Output Load in Range
6/5/24 21:44:12 Output Load Threshold Exceeded
6/5/24 21:42:39 Battery Discharged
6/5/24 21:41:56 Battery Charge in Range
6/5/24 21:17:51 Battery Discharged
6/5/24 21:17:36 Battery Charge in Range
6/5/24 21:16:39 Battery Discharged
What does this 'Battery Discharged' event mean?
We are not getting continuous power outages or any mains power issues.
I even had a controlled shut down happen on my, while using the PC, with no mains power issues happening, as follows:
5/30/24 17:38:56 <a href=https://www.apc.com/pcss>https://www.apc.com/pcss</a>
5/30/24 17:37:59 Communication Established
5/30/24 17:37:56 Monitoring Started
5/30/24 17:36:48 Monitoring Stopped
5/30/24 17:30:27 User Logged On
5/30/24 17:28:42 <a href=https://www.apc.com/pcss>https://www.apc.com/pcss</a>
5/30/24 17:27:44 Communication Established
5/30/24 17:27:42 Monitoring Started
5/30/24 17:23:30 Monitoring Stopped
5/30/24 17:23:28 Main Outlet Group commanded to: shutdown using delay
5/30/24 17:23:28 Shutdown process started
5/30/24 17:23:28 Low Battery
5/30/24 17:23:28 On Battery
5/30/24 17:21:36 Battery Discharged
5/30/24 17:21:35 Battery Charge in Range
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-06 11:49 AM . Last Modified: 2024-06-06 11:53 AM
Based on only the event logs provided by you this is what it means.
- Power Quality: Based on the event logs the system determined the input voltage, frequency, THD, was not acceptable. As such the system went into battery only mode.
The power quality / condition lasted much longer than the UPS battery could sustain and thus initiated a soft graceful shutdown via PCSS.
The other two events indicate the battery charging state when the battery was depleted and was recharged. Once fully charged the system indicated it was in range or fully charged.
The last event indicates at some point the connected load was above what the system could sustain. If you provide the data logs which show the same time period of the event logs you have provided here I can expand on this explanation if you like.
The data logs are those that indicate the input / output voltage, frequency, battery capacity, charging level, battery voltage, etc.
Let me know if this answered your question if not please do ask. If the information provided did answer your query please do mark this as resolved and mark this reply as a solution.
As this will help the next person asking the same. 👍
Cheers! 🍺
NOTE: You may change the sensitivity of the unit by following the user guide provided here in page 14. Set the sensitivity from med (default) to low.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-10 04:18 AM
How old is this unit and internal battery? The average service life of the battery is 2-5 years based on usage, temperature, power quality, and environmental conditions.
The cells can endure 260 full depletions as it shows battery health issues. If we assume the battery is not healthy you can test this out now and report back what happens.
Remove the USB cable that connects to the UPS and keep your computer off. Attach a few loads that won’t be harmed if the UPS does a hard shutdown.
Disconnect the AC Mains from the wall outlet. Use something to track how long the unit operates for until it completely shutdown.
Please report back what you see and observe doing this grid down / lights out test. Lastly, is there no data logs that show the input / output voltage, frequency, power, battery voltage, battery capacity etc?!?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-10 08:12 AM
Appreciate you taking the time to offer the image capture. When time permits simulate a grid down event / lights out by removing AC Mains from the wall.
Time how long the unit operates for with a steady 30% load until it automatically shuts down. Let the unit recharge the internal battery and review the event / data logs to see if there is a change in operating behaviour. 👍
In the interim I would reach out to APC Technical Support to request insight about your unit.
They may very well initiate a RMA for the unit because the event logs aren’t normal as it relates to the endless battery charge events.
NOTE: I have appended the full users manual for this unit. On page 14 please change the sensitivity to (Green) to allow a higher input voltage. The unit may be going into battery only mode as the input voltage is too high. Based on your data logs the input voltage is 250+ VAC.
Is your location 220, 230, 240 VAC? If 220 / 230 VAC I could see the unit constantly going into battery only mode. ☹️
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-10 12:21 PM
Okay, thanks. It's the UK, so 230 VAC, or generally 230 volts -6%, +10%
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-11 05:28 AM
Appreciate the confirmation your input voltage is 230 VAC. Would you kindly make the change as outlined in the user manual to a less sensitive voltage range.
Please do report back what you see and observe in both the event / data logs. APC Technical Support would have asked you to make this specific change as part of the troubleshooting process. 👍
Cheers! 🍺
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.