BX1300LCD - Repeated battery detach/battery attach events

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1300LCD - Repeated battery detach/battery attach events
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:56 AM

0 Likes
9
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:56 AM

BX1300LCD - Repeated battery detach/battery attach events

I'm using a BX1300LCD, and I keep getting the following messages from apcupsd:


2011-11-19 11:45:43 -0500 Battery disconnected.
2011-11-19 11:45:52 -0500 Battery reattached.
2011-11-19 11:45:56 -0500 Battery disconnected.
2011-11-19 11:49:13 -0500 Battery reattached.
2011-11-19 11:49:29 -0500 Battery disconnected.
2011-11-19 11:49:34 -0500 Battery reattached.
2011-11-19 11:49:38 -0500 Battery disconnected.
2011-11-19 11:49:55 -0500 Battery reattached.
2011-11-19 11:49:59 -0500 Battery disconnected.
2011-11-19 11:50:08 -0500 Battery reattached.
2011-11-19 11:50:12 -0500 Battery disconnected.


Over and over again. Meanwhile, the battery bar will flash and be empty, then go back to being solid and full. When it flashes, it also chirps.

What should I make of this? Is this just as simple as the battery needing to be replaced? The battery date is 10/06/2007, so I'm thinking that's probably it.

But before I drop $75 to replace this thing, I'd like to make sure the UPS itself hasn't gone faulty.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apcupsd
  • reattached
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
1
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

With assistance from the program developer, I've resolved the problem.

Apcupsd does have the ability to work via libusb instead of the Linux kernel's hiddev driver. Apcupsd and Vmware EXSi 5.0 seem to be much happier when used with libusb rather than hiddev. I've been running for 24 hours now without a single "Battery disconnected", "Battery reattached" error.

To make this change:
yum install libusb-devel.i386
./configure enable-usb with-generic-usb
make
make install

Also note that running this version of apcupsd will disconnect your UPS from the Linux kernel's hiddev driver so the previous apcupsd build not work again until you reboot.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

also clean the tabs on the battery pack.. a pencil eraser work well for this. Make sure that the mating connecters in the ups are clean and have not "spread apart" so the battery tabs make good contact.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

Can You Measure The Battery Voltage

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

Hi David,

Do you have another UPS that might be using the same battery? We had instances wherein after battery replacement the issue was fixed, if you have a battery to spare it would be best to try that one first. It could also be a faulty battery charger that fails to detect the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:25 AM . Last Modified: ‎2024-03-21 04:55 AM

Which version of apcupsd?

I don't think it is a battery error but a comm error. I am seeing the same events in v3.14.8 about every 30 minutes, just enough to be annoying.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

John -

If you've been getting this message and your UPS exhibits the battery disconnected behavior, chances are the UPS is at fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

I'm having the same problem. I'm using a backups ES550. I just swapped the ES550 for another unit and I still have the issue. The batteries in both units were replaced less than a year ago. I recently changed from a physical server to a virtualized server under VMware ESXi. I didn't have the issue prior to the change to EXSi. I can see VMware messing things up, but for only one this one message? I'm using apcupsd 3.14.10. on Centos.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
0
3302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

I've swapped the UPS for another identical unit. I see the same issue with both UPS units. I also looked at the trace file from apcupsd and I can see that other parameters in addition to the battery disconnected parameter also get set to zero and then quickly return to the actual value. I had no problems before I started using apcupsd under VMware ESXi. Neither UPS have any issue when using the APC windows UPS monitoring program. Doesn't seem like a UPS problem to me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

0 Likes
1
3305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-21 04:55 AM

With assistance from the program developer, I've resolved the problem.

Apcupsd does have the ability to work via libusb instead of the Linux kernel's hiddev driver. Apcupsd and Vmware EXSi 5.0 seem to be much happier when used with libusb rather than hiddev. I've been running for 24 hours now without a single "Battery disconnected", "Battery reattached" error.

To make this change:
yum install libusb-devel.i386
./configure enable-usb with-generic-usb
make
make install

Also note that running this version of apcupsd will disconnect your UPS from the Linux kernel's hiddev driver so the previous apcupsd build not work again until you reboot.

Reply

Link copied. Please paste this link to share this article on your social media post.

realivanjx
realivanjx
Cadet

Posted: ‎2024-06-11 11:17 AM

In response to Anonymous user
0 Likes
0
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-11 11:17 AM

it seems that the events for power failure and power restored are no longer logged to syslog with your build. when i disconnect the power the apcaccess indicates on battery status though. any idea on how to fix the syslog?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore