Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is my Back-UPS 550G faulty - not switching back to mains after outage ?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is my Back-UPS 550G faulty - not switching back to mains after outage ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
148
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:32 AM

1 Like
5
4975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:32 AM

Is my Back-UPS 550G faulty - not switching back to mains after outage ?

Having some strange behavior with my brand new 550G.

UPS is setup to support a Windows 7 machine, running powerchute personal edition. Software is configured to shutdown PC after 5 minutes.

When I disconnect the mains power, the battery kicks in keeping the PC alive, and after 5 minutes - the PC is powered down into hibernation.

When I reconnect the mains power -

1 the PC starts rebooting out of hibernation but display on UPS remains showing battery...

2 the PC once fully booted, sits there for 20 seconds or so - and then the UPS completely disconnects the PC - shutting it down power cut style - crashing it.

3 After another 10 seconds, the display on the UPS then flicks from battery to mains power display.

this behavior is totally repeatable and totally wrong ....

Any suggestions  ? Mains power is quite normal voltage - 240V (UK)

Thanks,

Julian

Birmingham, UK


Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 550g
  • back-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

0 Likes
0
4968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

Hi Julian,

The symptom you have indicated seeing during your testing is not what is expected from the unit during normal operation. I believe the issue may lie in the method we are using to test this device. By removing the plug from the wall, we are eccentially resetting the unit's connection to neutral and earthground. In doing so, I believe we are effectively reinitiallizing the computer powersupply. If this same scenario were to occur naturally while still connected to the utility outlet, the computer would not return to an "ON" status until the UPS had completely cycled power to iteself and returned to an Online state. This scenario would occur for both Back-UPS and Smart-UPS units. The best way to test the operation of the units would be to lower or remove utility power with the use of a Variac device. This would be the best method for simulating a poweroutage.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:32 AM

0 Likes
0
4968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:32 AM

I think you might be interrupting the pre-programmed UPS timeline while the UPS is in the middle of its reboot cycle. So I think it is working as designed.

Just because you reconnect the mains power after the shutdown/hibernation begins, it does not mean the UPS has completed its process. Please review the timelines below and I'd try your testing again and leave the UPS unplugged for several minutes and let it turn off completely and go to low voltage sleep mode and then plug it back in. Don't plug it immediately back in as soon as the computer hibernates.

Shutdown time line, software not installed:

1. UPS goes to battery, the on battery beep sounds

2. The UPS will sound the on battery beep until it reaches the last few minutes of run time when the battery has been depleted.

3. When the unit reaches the last few minutes of battery life it will then sound its low battery alarm.

4. Just before the battery is completely exhausted the ups will turn itself off.

5. If the UPS went to battery due to a brown out the unit at this point will be in LVSM (low voltage sleep mode) until the voltage becomes acceptable again.



PowerChute Personal Edition default shutdown time line:

1. UPS goes to battery and PCPE starts its preserve battery power counter.

2. When the counter expires it sends a command to the UPS to start counting its turn off delay and then commands the OS to shutdown.

3. The operating system shuts down and the UPS continues to count its turn off delay. (Once the UPS finishes counting its turn off delay it will reboot and nothing can stop this from happening.)

4. The UPS cuts power to the outlets then rechecks to see if the incoming power is acceptable. If it is not, it waits there until power returns.

5. If the UPS went to battery due to a brown out the unit at this point will be in LVSM until the voltage becomes acceptable again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:32 AM

0 Likes
0
4968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:32 AM

Thanks for the info... Much Appreciated...smile

Hmm.. sounds like this is a design fault then - if power returns before the UPS reboot cycle is complete - the UPS will effectively un-hibernate and then crash a protected device... Not Good...

If I programme my PC to shut down after 5 minutes, and then there is a one minute reboot cycle - I am effectively unprotected for any power cuts that last between 5 & 6 minutes...

Is this correct ?

Ideally, if the UPS is in its reboot cycle - and power returns -  it should NOT provide any power to connected devices until reboot is complete - the would solve everything...

Does the smart line of UPS have the same behavior ? I may just upgrade....

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

0 Likes
0
4968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

Hi sbsnet,

Hopefully I can help to clarify the need for this function. Once the Powerchute software reaches the user designated parameters for shutdown, the Powerchute software initiates a system Shutdown as if the User themselves had initiated a system shutdown. Just like the User initiated Shutdown, this can not be disrupted. Interruption of the system shutdown at this point would result in system errors and loss of materials designated for hibernation. In addition, utility power when lost may fluctuate randomly while the electrical provider is attempting to re-stabilize. A momentary return of utility power may not be sufficient enough to support the UPS in the Online state. Due to the limited runtime present in the UPS and the inherent obligation of the unit to protect the computer and the data contained there-in, interrupting the System Shutdown prematurely would be considered an unnecessary risk, as the UPS may not have retained enough "runtime" to initiate and complete a System Shutdown a second time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

0 Likes
0
4968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

Thanks for that.

For the record - how long is the turn off delay for a back-ups 550g (ie how long before the UPS reboots upon receiving a reboot signal from the PCPE software) ?

I guess its been designed to be just long enough for majority of slow devices to go into hibernation...

For the Smart range of UPS - do they behave in the same way ? and if normal power resumes BEFORE reboot of UPS has occured - will protected device get re-awoken and then promptly subjected to a power cut - which is what i'm observing ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

0 Likes
0
4969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:47 PM . Last Modified: ‎2024-03-21 12:31 AM

Hi Julian,

The symptom you have indicated seeing during your testing is not what is expected from the unit during normal operation. I believe the issue may lie in the method we are using to test this device. By removing the plug from the wall, we are eccentially resetting the unit's connection to neutral and earthground. In doing so, I believe we are effectively reinitiallizing the computer powersupply. If this same scenario were to occur naturally while still connected to the utility outlet, the computer would not return to an "ON" status until the UPS had completely cycled power to iteself and returned to an Online state. This scenario would occur for both Back-UPS and Smart-UPS units. The best way to test the operation of the units would be to lower or remove utility power with the use of a Variac device. This would be the best method for simulating a poweroutage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore