Is it possible to use a single eu2000i with uts10bi switch?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is it possible to use a single eu2000i with uts10bi switch?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
5
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

Is it possible to use a single eu2000i with uts10bi switch?

Is it possible to use a single eu2000i with uts10bi switch? I was thinking I could run it through "backup 2", in place of a UPS.  I wanted the option of more circuits and to be able to use either the Honda or my larger GP5500 120/240.  Thanks in advance!

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

Certainly you could use a small 120 volt generator for the source to the "backup 2" input, but keep in mind that the backup 2 input is limited to 15 amps total load, and you will only be able to power circuits 2 through 8 from the backup 2 input. By design, the expected source for the backup 2 input is a UPS sourced from the front panel convenience outlet (connected to circuit 1) and powered under "normal" conditions by utility power input, or the backup 1 source, so it will not provide power to itself (the assumed UPS input). Also, because backup 2 is 120 volt only, circuits 9 and 10 will not be activated because they are used together as a 240 volt output circuit.

I don't understand what you mean by "the option of more circuits", can you clarify?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

Ah, Yes, if GWN was working from the baseline of a UTS6H with a 120v Backup 1 input and all 6 120v outputs, then the UTS10BI would provide 1 additional 120v output when using ONLY the Backup 2 input. Remember, none of the UTS6 models or the UTS10BI will activate output 1 when the only input source is Backup 2. While not significant when using the EU2000i (rated around 16A?), he would sacrifice the 30A rating of the UTS6H Backup 1 input for the 15A rating of the Backup 2 input on all models. For more outputs, the UTS10BI provides 8 120v outputs and a single 240v output when the Backup 1 input is connected to a 240v capable generator.

Your suggestion of connecting the L1 and L2 inputs together into the Backup 1 input from the single "L1" of the EU2000i L5 outlet, while interesting and likely possible with most "dumb" transfer switches, will not work here because the monitoring circuitry within the UTS (either 6, 6BI or 10BI) will declare a Backup 1 input fault condition of 120v, or more likely 0v from L1 to L2 where it should measure 240v, and not source any outputs from Backup 1, even if the UTS can operate at all!

Message was edited by: Wayne I

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

Yes I agree with Boatingtrb, you CAN use an EU2000 with the UTS10BI.  While it's true that the UTS10 wants 240V on the utility side, and it will not power up with a split 120V on backup 1, it WILL run with a UPS connected to backup 2.  You must use a UPS for this to work.  If the power goes out, UPS keeps the electronics hot.  I took a single phase 120V source, doubled the hot legs into the backup 1 input and the "generator" input was recognized.  Now, that being said if you do this, you best not try to power anything on the 240V circuit.  I decided on this UTS because it had 8 120V circuits available while the UTS6H only has 6.  I have to 240V devices in my house, so this works great for me.  In theory you can use circuits 9 and 10 as 120V as well if you want but only if the "generator" is running, not the UPS.  Just like Todd above, I wanted the ability to use a 220V generator later in life, and this was a great solution.

-Ryan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

I have done it with the UTS10BI & EU2000i using a pigtail to go from L5-30 (gen side) to L14-30 (UTS side) and it works just fine powering the UTS panel and circuits 1 through 8 on backup1.

Works fine & still gives me the option to plug in a 220v gen because the pigtail combines the 2 hot leads.

-Todd

ps I have circuits 9 & 10 wired for the kitchen disposal & the cloths washer (9 & 10 respectively) and they work just fine when I plug in a 220v generator.  So, with the EU2000i, I lose use of the disposal & cloths washer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

Is it possible to use a single eu2000i with uts10bi switch? I was thinking I could run it through "backup 2", in place of a UPS.  I wanted the option of more circuits and to be able to use either the Honda or my larger GP5500 120/240.  Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

0 Likes
0
1356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:56 PM . Last Modified: ‎2024-03-20 12:33 AM

Certainly you could use a small 120 volt generator for the source to the "backup 2" input, but keep in mind that the backup 2 input is limited to 15 amps total load, and you will only be able to power circuits 2 through 8 from the backup 2 input. By design, the expected source for the backup 2 input is a UPS sourced from the front panel convenience outlet (connected to circuit 1) and powered under "normal" conditions by utility power input, or the backup 1 source, so it will not provide power to itself (the assumed UPS input). Also, because backup 2 is 120 volt only, circuits 9 and 10 will not be activated because they are used together as a 240 volt output circuit.

I don't understand what you mean by "the option of more circuits", can you clarify?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of