Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to know if the battery is dead?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • How to know if the battery is dead?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
tbarbette
Crewman tbarbette
Crewman

Posted: ‎2024-04-01 12:07 PM . Last Modified: ‎2024-04-02 12:35 AM

0 Likes
3
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-01 12:07 PM . Last Modified: ‎2024-04-02 12:35 AM

How to know if the battery is dead?

Hi all,

 

My UPS is cutting power in a few seconds when the main power is off. But at the same time the battery health seems to be okay. Here's the result of upsaccess in Linux :

 

APC : 001,036,0873
DATE : 2024-04-01 20:06:49 +0200
HOSTNAME : tomsrv
VERSION : 3.14.14 (31 May 2016) debian
UPSNAME : tomsrv
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2024-04-01 13:43:42 +0200
MODEL : Back-UPS XS 700U
STATUS : ONLINE LOWBATT
LINEV : 228.0 Volts
LOADPCT : 32.0 Percent
BCHARGE : 100.0 Percent
TIMELEFT : 0.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : Medium
LOTRANS : 140.0 Volts
HITRANS : 300.0 Volts
ALARMDEL : 30 Seconds
BATTV : 13.6 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x05000048
SERIALNO : 3B1938X67864
BATTDATE : 2019-09-20
NOMINV : 230 Volts
NOMBATTV : 12.0 Volts
NOMPOWER : 390 Watts
FIRMWARE : 924.Z5 .I USB FW:Z5
END APC : 2024-04-01 20:07:42 +0200

 

At the same time there is a problem with USB, it takes multiple hours before the UPS is accessible in Linux and I see some problems in dmesg. On Windows it's okay though. That makes me think there could be a problem with the UPS itself, and not just the battery. Still a few month ago the battery lasted for half an hour (full capacity).

 

I did a test with a 8W bulb (the capacity is shown to be 1% of the max current that can be drained). PowerShute on Windows says it will hold 14 minutes, but actually after 5 minutes the rapid beep starts. After which the UPS stops. Then at restart there is a continuous beep for like 30 seconds. And then it's okay again. Does that mean the battery is dead? Or it might be the whole UPS?  Because I never saw the button flashing red, and selftests are totally fine.

 

Thanks for the help !

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-02 08:33 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-02 08:33 AM

The rated service life of the batteries is 3-5 years and is based on usage, temperature, and environmental variables. If the batteries are 3-5 years old it’s time to consider a replacement. 

You can perform a couple of simple tests to determine the state of health of the batteries. 

- Self Test: Generally speaking this test will conduct a POST on the entire system. It will also perform a simple load test on the battery. If it fails immediately the battery is toast and needs to be replaced. 

- Load Test: You can do this one of two ways either via the Power Chute software where it completes the battery calibration or simply pulling the AC Mains from the wall.

 

In both cases there should be at least 30% attached load at the output. If it’s more like (real world) attached hardware even better. If you pull the plug and the unit shuts down immediately or a few seconds the battery is toast - replace! ☝️

 

If the unit operates for X minutes compare it to the APC Runtime Calculator. If the calculator indicates Y load should offer you 30 minutes with Y load and you only see 5 minutes for example - battery is toast - replace. 

If however the system operates for 20 minutes vs 30. It’s time to set aside finances to replace the batteries in the near future of your choosing.

 

Based on your description the battery is toast . . . 😢

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-02 08:33 AM

0 Likes
0
3037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-02 08:33 AM

The rated service life of the batteries is 3-5 years and is based on usage, temperature, and environmental variables. If the batteries are 3-5 years old it’s time to consider a replacement. 

You can perform a couple of simple tests to determine the state of health of the batteries. 

- Self Test: Generally speaking this test will conduct a POST on the entire system. It will also perform a simple load test on the battery. If it fails immediately the battery is toast and needs to be replaced. 

- Load Test: You can do this one of two ways either via the Power Chute software where it completes the battery calibration or simply pulling the AC Mains from the wall.

 

In both cases there should be at least 30% attached load at the output. If it’s more like (real world) attached hardware even better. If you pull the plug and the unit shuts down immediately or a few seconds the battery is toast - replace! ☝️

 

If the unit operates for X minutes compare it to the APC Runtime Calculator. If the calculator indicates Y load should offer you 30 minutes with Y load and you only see 5 minutes for example - battery is toast - replace. 

If however the system operates for 20 minutes vs 30. It’s time to set aside finances to replace the batteries in the near future of your choosing.

 

Based on your description the battery is toast . . . 😢

Reply

Link copied. Please paste this link to share this article on your social media post.

tbarbette
Crewman tbarbette
Crewman

Posted: ‎2024-04-07 12:17 AM

0 Likes
1
2978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-07 12:17 AM

Thanks! I changed the battery, and after resetting the date with PowerChute the APC works as new. That last part was not obvious for me though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-08 08:15 AM

In response to tbarbette
0 Likes
0
2977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-08 08:15 AM

If the information provided up above helped in the resolution please mark it as solved. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore