Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How do I start a SURT10000XLI with low batteries(<50V) ??

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • How do I start a SURT10000XLI with low batteries(<50V) ??
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
4
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

How do I start a SURT10000XLI with low batteries(<50V) ??

I have a number of SURT10000XLI, where the batteries are lower than 50V, some are even below 40V. The UPS does not seem to start, unless you have 4 batteries, with at least 80V each. Are there any tricks to get the UPS charger working if your batteries are lower than 40 - 50V ???

Kind regards

Olebenny

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

i don't think so and then you wouldn't want to necessarily try and charge those batteries that have been sitting at low voltage and cause more problems (i.e. overcharge, thermal runaway in extreme circumstances). my best recommendation is to get some fresh batteries for this UPS and if they are stored for a long time, adhere to battery storage recommendations outlined in the knowledge base @ http://www.apc.com/site/support/index.cfm/faq/ , article ID FA156516 (Battery Discharge During Storage) & FA157446 (Battery Damage When Battery Is Left Discharged)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

i don't think so and then you wouldn't want to necessarily try and charge those batteries that have been sitting at low voltage and cause more problems (i.e. overcharge, thermal runaway in extreme circumstances). my best recommendation is to get some fresh batteries for this UPS and if they are stored for a long time, adhere to battery storage recommendations outlined in the knowledge base @ http://www.apc.com/site/support/index.cfm/faq/ , article ID FA156516 (Battery Discharge During Storage) & FA157446 (Battery Damage When Battery Is Left Discharged)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

Hello Angela

Thanks for replying.

So the answer is no ??

Which means you need a set of new batteries, if your UPS runs on  battery until the batteries are flat.

After this, you can't start the UPS without a set of new batteries ???

Kind regards

Ole

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

No - when the UPS runs on battery, it does not discharge them below a certain voltage where then it knows it can charge them back up.

If your batteries are below that level (improperly stored or not periodically charged), they cannot charge back up and are beyond the point of return. As batteries get older over time, I think they become more sensitive to that voltage point and after the more number of deep discharges, the higher the risk over the years to not be able to charge back up, thermal runaway, etc. Batteries consists of chemicals as you may know so after time, the chemical reactions don't work so well anymore.

Reply

Link copied. Please paste this link to share this article on your social media post.

seb206
seb206
Explorer

Posted: ‎2024-09-13 09:20 AM

0 Likes
0
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-13 09:20 AM

Hello, I have the same issue, what is the solution?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore