Help with setup and Back-UPS information

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Help with setup and Back-UPS information
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS
product field
Schneider Electric
Back-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Microfiche
Microfiche
Cadet

Posted: ‎2025-02-15 08:30 AM

0 Likes
2
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-15 08:30 AM

Help with setup and Back-UPS information

Hey all, sorry if this is a bit long, but want to ensure I am not missing important details.
I have two APC UPS units, a Smart UPS 750 (SMT750) and a BackUPS Pro (BR1000MS).
These are protecting 2 Windows 11 computers, a QNAP NAS, a Raspberry Pi and a router.
Both UPS units are connected to the same power receptacle. I slapped together a diagram below.


As there is no network connectivity natively on these 2 UPS units, I have connected the Back-UPS to the Raspberry Pi via the USB serial cable, and the Smart-UPS to PC-2 via the USB serial cable.
I am running Powerchute serial shutdown on PC-2, with a script that shuts down PC-1 as part of the PC-2 shutdown process.


The Raspberry Pi connected to the Back-UPS is running NUT, and the QNAP NAS is connected to the Back-UPS over the network for shutdown purposes and also plugged into it.


PC-1 is plugged into the Smart-UPS, and PC-2 is plugged into the Back-UPS to balance the load between the UPS units and provide maximum run time. So yes, PC-1 will shut down if the Back-UPS loses power, even though it is physically plugged into the Smart-UPS.


Currently I have the Raspberry Pi and the router plugged into the Smart-UPS.
The only problem I had when testing the shutdown is that the Raspberry Pi and router are being shut down during the shutdown process on the Smart-UPS. I didn't realize that the outlets on the UPS are actually turned off during the serial shutdown process.

 

So what happens on the Back-UPS when power is lost and Powerchute serial shutdown is NOT connected?
Will the outlets stay powered as long as the battery has power? I can't find anything in the manual. If that is the case, I can plug the Raspberry Pi and the router into the Back-UPS instead and everything should work fine.


Also - assuming I don't want to invest more in a new network connected UPS, is this a reasonable solution?

 

UPS setup.png

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
fredkm
Lieutenant fredkm Lieutenant
Lieutenant

Posted: ‎2025-02-17 12:30 AM . Last Modified: ‎2025-02-17 12:31 AM

0 Likes
1
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 12:30 AM . Last Modified: ‎2025-02-17 12:31 AM

PowerChute Serial Shutdown will turn off the outlet group powering the server as part of the shutdown process. In your setup this is PowerChute Serial Shutdown installed on PC-2 that will turn off the connected SMT750.

 

Your Back-UPS currently is not controlled by PowerChute Serial Shutdown, so it will keep powering connected equipment until the battery drains.

 

The new 1.3 version has an option in the Shtudown Settings page to not turn off the UPS, but this option is only made available for connected Back-UPS (and not Smart-UPS). SMT750 only has a single main outlet group which is always turned off during shutdown process. If you connect a higher-end Smart-UPS, with multiple outlet groups, you can configure PowerChute Serial Shutdown to include/exclude outlet groups from the shutdown process. This is great for secondary equipment you want to keep powered on.

 

So, what's the reasoning behind PowerChute Serial Shutdown turning off the outlet group powering the server you may wonder. On most Smart-UPS you can configure outlet groups to automatically turn on again when power is restored. This comes in handy when you configure your server to auto-restart after power outage. As soon as power returns, the UPS outlet group turns on, and your server will restart. Of course this will only work if the outlet group was turned off first. If the outlet group remains powered on during an outage then your server will not auto-restart if power returns.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
fredkm
Lieutenant fredkm Lieutenant
Lieutenant

Posted: ‎2025-02-17 12:30 AM . Last Modified: ‎2025-02-17 12:31 AM

0 Likes
1
1228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 12:30 AM . Last Modified: ‎2025-02-17 12:31 AM

PowerChute Serial Shutdown will turn off the outlet group powering the server as part of the shutdown process. In your setup this is PowerChute Serial Shutdown installed on PC-2 that will turn off the connected SMT750.

 

Your Back-UPS currently is not controlled by PowerChute Serial Shutdown, so it will keep powering connected equipment until the battery drains.

 

The new 1.3 version has an option in the Shtudown Settings page to not turn off the UPS, but this option is only made available for connected Back-UPS (and not Smart-UPS). SMT750 only has a single main outlet group which is always turned off during shutdown process. If you connect a higher-end Smart-UPS, with multiple outlet groups, you can configure PowerChute Serial Shutdown to include/exclude outlet groups from the shutdown process. This is great for secondary equipment you want to keep powered on.

 

So, what's the reasoning behind PowerChute Serial Shutdown turning off the outlet group powering the server you may wonder. On most Smart-UPS you can configure outlet groups to automatically turn on again when power is restored. This comes in handy when you configure your server to auto-restart after power outage. As soon as power returns, the UPS outlet group turns on, and your server will restart. Of course this will only work if the outlet group was turned off first. If the outlet group remains powered on during an outage then your server will not auto-restart if power returns.

Reply

Link copied. Please paste this link to share this article on your social media post.

Microfiche
Microfiche
Cadet

Posted: ‎2025-02-17 07:31 AM

In response to fredkm
1 Like
0
1197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 07:31 AM

Perfect - that is what I needed to know regarding the Back-UPS!

And yeah - I get why they set it to shut they shut the outlets off, I had just never thought about it before, as this type of situation had never come up. Appreciate the help! I have invested about as much as I care to in this system currently, so if this work, I don't have to buy another UPS! Yay!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore