[Help] Why my UPS LS 700 just works with battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • [Help] Why my UPS LS 700 just works with battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
7
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

[Help] Why my UPS LS 700 just works with battery?

Hi everyone.

I have an UPS from APC "LS 700" (Serial: NB0140162004) the original battery it's gone so i bought a replacement (RBC17). But now, the UPS just works with the battery, the indicator led "online" is off BUT i can connect my printer there and the printer works...also if i connect my cpu and monitor on the battery's outlet they are on,..if i disconnect the UPS from the energy my printer goes off (obviusly) and my CPU and monitor keeps on til the battery runs out of energy. But if i keep connected the UPS to the power line the printer, CPU and monitor keeps on about 15 minutes because the battery runs out of energy even if the UPS is connected to the power line the UPS goes off ! ! ! And also i have installed the powerchute to see the status of my UPS and it says "just working with battery" or something...Does someone knows what is going on with my UPS ?

Thank you so much.

Best regards, Felipe

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 700
  • backup
  • battery
  • line
  • ls700
  • outlet
  • power
  • ups
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

Thanks for the pictures. The voltage is 130 volts according to the UPS.

Can you check under Configuration and look at the settings for Voltage and Sensitivity. I am more interested in voltage to see what the transfer ranges are set to in there. I wonder if its going to battery since you're seeing 130V and it is more than the nominal 120V. It could be the voltage was even higher and has gone down but not cleared the hysteresis (like a buffer) window.

It also might be a good idea to see if the voltage is high as 127-130V in other outlets at your location.

Lastly, have you just tried turning off and then on? If the UPS won't turn back on, it doesnt like the power you'll have to cold start it which is holding down the power button until it starts on battery power.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

Could you let us know when this stopped working specifically? Was it after you replaced the battery in the UPS?

Have you tried plugging the UPS into different wall outlets? What does PowerChute is the last transfer to battery reason? What does the input voltage show as?

A screenshot might be helpful of your PowerChute status by selecting current status on the left under Monitor System? See below for the screen I'd like to see or know the information from.

http://www.file-shop.com/Images/Misc/apc_idle.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

Thanks for the update.

UPS connected to the powerline and mode "OFF"

1174_IMG00098-20130523-1249.jpg

UPS connected to the Power Line and mode "ON"

1175_IMG00099-20130523-1250.jpg

Voltage on battery outlet and mode "ON"

1176_IMG00100-20130523-1251.jpg

Screen Capture PowerChute

1177_pc.JPG

I don't know exactly when just stop working properly.

Thank you

Best Regards, Felipe

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
1566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

Thanks for the pictures. The voltage is 130 volts according to the UPS.

Can you check under Configuration and look at the settings for Voltage and Sensitivity. I am more interested in voltage to see what the transfer ranges are set to in there. I wonder if its going to battery since you're seeing 130V and it is more than the nominal 120V. It could be the voltage was even higher and has gone down but not cleared the hysteresis (like a buffer) window.

It also might be a good idea to see if the voltage is high as 127-130V in other outlets at your location.

Lastly, have you just tried turning off and then on? If the UPS won't turn back on, it doesnt like the power you'll have to cold start it which is holding down the power button until it starts on battery power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:56 AM

1178_pc2.JPG1180_pc3.JPG

WOW just about configuration. I just set up the voltage over 130 V and now the UPS status it's like yours.

---------------------------------------------------------------- (:  ❤️1181_pc4.JPG

Thank you so much ! ! ! Close this thread or whatever be

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:55 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:55 AM

laughing great!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:55 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:55 AM

Hi, i am here once again.

The problem is that the UPS didn't saved the configuration that i made in the PowerChute or how does it works that ? i set-up the voltage at 135VAC as maximum and 106VAC as minium. I'm running the APC and the PowerChute shows 127VAC as before,

How can i save my configuration or how come that ?

Thank you

Best Regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:55 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 PM . Last Modified: ‎2024-03-21 12:55 AM

once you set it and press Apply at the bottom of the screen, it should stay and remain saved on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore