[Help]Smart UPS BK650-CH frequent communication failure with Buffal NAS LS-QVL

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • [Help]Smart UPS BK650-CH frequent communication failure with Buffal NAS LS-QVL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 PM . Last Modified: ‎2024-03-21 12:54 AM

0 Likes
1
1283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 PM . Last Modified: ‎2024-03-21 12:54 AM

[Help]Smart UPS BK650-CH frequent communication failure with Buffal NAS LS-QVL

Connecting the BK650-CH UPS with a NAS Buffalo LS-QVL which running on a Linux,,I met the following issue after running some hours( duration < 3 hours):

   1.  Enalbe the "Synchronization with UPS" option on the admin WebUI;

   2.  "USB Connection Type" only has one option which is “USB Port(APC Style)”--So ,I guess this buffalo NAS should have passed a sort of certifcation with APC UPS as the screenshot:

               1190_ups_setting.jpg

   3.  Max 3 hours after "Synchroniztion with UPS" has been enalbed successfully, the NAS will enther a "fake-crash" state which means all the LEDs display correctly so I can say functionalities should be ok ,meanwhile I CAN PING the NAS successfully via PC, but I CAN NOT login to its WebUI and I can NOT power off the NAS by pressing power key--so I can't ensure the embeded functionalities is working correctly or not;

    4. The only thing  I can do is to remove the plug from the outlet at this time.

    5.  After the NAS has been re-powered on, I can check the kernel log as attached below;

   6. If I disable the "Synchronization with UPS" , the NAS can work correctly for at least 2 days( the lognest duration I tested )


  The ps information in the kernal:

   1191_ups_ps.jpg

   The kernal log is:

May 23 07:48:18 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:48:40 SeanMediaRepo upsd[24812]: UPS [ups] data is no longer stale

May 23 07:48:40 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 07:48:40 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost lost

May 23 07:49:12 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost established

May 23 07:49:44 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:49:44 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 07:49:44 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost lost

May 23 07:49:44 SeanMediaRepo upsd[24812]: UPS [ups] data is no longer stale

May 23 07:49:44 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost established

May 23 07:49:44 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:50:04 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Server disconnected

May 23 07:50:55 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost lost

May 23 07:50:57 SeanMediaRepo upsmon[24810]: Set username on [ups@localhost] failed: Server disconnected

May 23 07:50:57 SeanMediaRepo upsd[24812]: User admin@127.0.0.1 logged out from UPS [ups]

May 23 07:50:57 SeanMediaRepo upsd[24812]: write() failed for 127.0.0.1: Broken pipe

May 23 07:51:46 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Driver not connected

May 23 07:51:59 SeanMediaRepo upsd[24812]: UPS [ups] data is no longer stale

May 23 07:52:27 SeanMediaRepo upsd[24812]: write() failed for 127.0.0.1: Broken pipe

May 23 07:52:32 SeanMediaRepo upsd[24812]: User admin@127.0.0.1 logged into UPS [ups]

May 23 07:52:32 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost established

May 23 07:52:32 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:52:35 SeanMediaRepo upsd[24812]: UPS [ups] data is no longer stale

May 23 07:53:02 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 07:53:26 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:53:26 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost lost

May 23 07:53:26 SeanMediaRepo upsd[24812]: UPS [ups] data is no longer stale

May 23 07:53:26 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:53:26 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost established

May 23 07:53:26 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 07:53:26 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost lost

May 23 07:53:26 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 07:53:30 SeanMediaRepo last message repeated 4 times

May 23 07:53:30 SeanMediaRepo upsd[24812]: UPS [ups] data is no longer stale

May 23 07:55:04 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost established

May 23 07:55:56 SeanMediaRepo upsd[24812]: Data for UPS [ups] is stale - check driver

May 23 07:57:42 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 07:57:42 SeanMediaRepo upsmon[24810]: Communications with UPS ups@localhost lost

May 23 07:58:14 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 08:01:25 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 08:06:19 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 08:17:05 SeanMediaRepo upsmon[24810]: Poll UPS [ups@localhost] failed - Data stale

May 23 08:29:56 SeanMediaRepo syslogd 1.5.0: restart.

May 23 08:29:56 SeanMediaRepo kernel: klogd 1.5.0, log source = /proc/kmsg started.

May 23 08:29:56 SeanMediaRepo kernel: Cannot find map file.

May 23 08:29:56 SeanMediaRepo kernel: Loaded 35316 symbols from 10 modules.

May 23 08:29:56 SeanMediaRepo kernel: Booting Linux on physical CPU 0

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • bk650
  • communication
  • failure
  • linux
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 PM . Last Modified: ‎2024-03-21 12:54 AM

0 Likes
0
1283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 PM . Last Modified: ‎2024-03-21 12:54 AM

We can help you support the UPS side of this but we don't know the Buffalo NAS - have you reached out to Buffalo yet?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 PM . Last Modified: ‎2024-03-21 12:54 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 PM . Last Modified: ‎2024-03-21 12:54 AM

We can help you support the UPS side of this but we don't know the Buffalo NAS - have you reached out to Buffalo yet?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore