H15 trim

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • H15 trim
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
6
1670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

H15 trim

Periodically, my H15 unit goes into trim mode (possibly from seeing a voltage higher than 124V). Looking at the display, I see that the Vin (voltage in) is 124 and the Vout (voltage out) is 117. The unit stays in trim mode until I turn on a device plugged into the H15. Then, the unit goes out of trim. The Vin remains at 124 and the Vout becomes 124 as well. Is this normal? I'm concerned that during long off times of connected components, the unit is working unnecessarily to trim voltage. Not sure if this will effect the life of the unit. Please advise. Thanks

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

Thanks Buzz. This information is helpful.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

What do you have the AVR range set to (wide, normal, narrow)?

Either way, it shouldn't affect the life of the unit. It's more of an issue if it goes in and out of trim/boost repeatedly, all day long, because that will wear out the relay faster. Otherwise what you're describing doesn't sound like an issue in terms of life expectancy.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

Hi Buzz. It is currently set to narrow. But why is the unit staying in trim mode when there is no need (i.e. after input voltage returns to 124)?

Actually, the unit is not going in and out of trim. Once in trim, it stays there (despite normal voltage being supplied) until there is a load placed on the unit by turning on a component plugged into the H15 (like my TV). Then the trim turns off immediately.

I'm in the room the H15 is in very frequently. It is unusual for the unit top go into trim, maybe once or twice per week. I notice it because it stays in trim until I turn something on.

This unit has a wiring ok light issue and it will be replaced by APC when units without this issue are available. I wasn't sure if this trim situation is typical of H15's, or if there is something odd with this H15.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

Yeah, I gotcha. Basically it goes into trim mode due to high(ish) voltage - 125v on narrow - and it stays in trim until the hysteresis threshold (5v) has been reached. Then you turn your TV or whatever on, which causes a very brief sag in the voltage, so brief the unit's display may not even reflect it. Afterward the voltage goes back to 124v, but because of that very brief sag, it's outside of the hysteresis window and 124v is acceptable (below 125v) so it stays "online" without trimming at that point. Sounds like normal behavior, I tested it myself and it does the same thing. πŸ™‚

I'm not sure how familiar you are with hysteresis, but basically it's a window where the unit will stay performing as it is so it doesn't keep switching back and forth when the voltage fluctuates slightly but rapidly. In this instance, the window is 5v, so once the unit starts trimming at 125v, it won't stop trimming until the voltage is reduced by 5v to 120. For example, you wouldn't want the unit to keep going in and out of trim mode with the voltage changing slightly from 124 to 125, as electricity is wont to do. The brief sag in voltage when you turn on your equipment reduces the voltage enough to get it to stop trimming, and then the voltage is fine at 124v again. Make sense?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

Buzz, I understand your post. I also changed the setting from narrow to normal. Same thing is happening. Is this still normal?

What is the window on the normal and wide setting (is it still 5v)? Is the window the same for boost and trim? Thanks!

P.S. At what voltage does the H15 begin trimming voltage in narrow, normal and wide? At what voltage does the H15 unit begin boosting voltage in narrow, normal and wide?

Message was edited by: apcme

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

Yes, it's most likely still normal, since the hysteresis windows are larger with the wider AVR ranges. Here are the ranges:

Narrow: 102-132v, regulates to 120 +/- 5%
Normal: 97-139v, regulates to 120 +/-10%
Wide: 92-145v, regulates to 120 +/- 15%

Playing with an H15BLK, here's where boost/trim seem to kick in: (apparently I can't make nice table-like layout)

AVR Setting / Boost / Trim / Hysteresis
Narrow: 113v / 125v / 5v
Normal: 110v / 128v / 10v
Wide: 108v / 130v

Hysteresis was harder to determine on wide since it regulates to +/-15%... but it would stay in trim/boost mode for awhile even back at 120v before going back to normal operation. Sometimes I had to bring it below 120v, where it would start to boost and then realize voltage was fine before coming online.

I'd leave it on narrow, personally.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

0 Likes
0
1670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:58 PM . Last Modified: β€Ž2024-03-20 05:54 AM

Thanks Buzz. This information is helpful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore