Firmware upgrade path for Smart-UPS 500 (SCL500RM1UNC)
We have 4 x Smart-UPS 500 (SCL500RM1UNC)
all running the stock ID1029UPS 02.5 firmware
These need updating to a newer firmware, to add support for newer TLS standards. Otherwise the web interface isn't opening on HTTPS.
My attempts to go to the latest ID1029UPS 15.1, results in the error "Rated Output Voltage set failed".
Is there a recommended upgrade path via interim firmware versions? Or is there a solution to fix this error.
Many thanks
- Labels:
-
Home & Office - UPS & Software
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-16 04:46 AM
All four UPSs upgraded successfully to NMC v7.0.8.
This fixed the error message on the other firmware, although I haven't upgraded yet due to them needing to go offline to upgrade.
The HTTPS connection was still broken after this, but deleting the Web -> SSL Certificate and rebooting fixed this issue as well.
Many thanks for the help
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-08 04:10 PM . Last Modified: 2023-01-08 04:10 PM
Hi @gmax
May I please know what method did you use to upgrade the UPS firmware? Regarding the HTTPS issue, may I know the exact issue that you are having as well as the browser that you are using and the firmware loaded on the network management card?
There is two firmware for your UPS, the UPS, and the NMC firmware.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-09 03:13 AM
Certainly...
The update was done through the HTTP web interface. I also tried through the Windows app, that didn't work either, although I don't remember the error message.
The HTTPS version of the interface won't open in either Firefox or Edge (Chromium) on Ubuntu 22.04, and returns the error:
Secure Connection Failed
Error code: PR_CONNECT_RESET_ERROR
I'm only guessing it's an error related to TLS version as it similar to another issue we had.
The network card details are:
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-10 12:23 AM
Kindly see the links provided below to upgrade the NMC firmware that you have to v7.0.8.
Video: How do I upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device ...
UPS Network Management Card v7.0.8 Firmware for Smart-UPS & Galaxy 3500 with AP9630/31/35 - SFSUMX70...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-16 04:46 AM
All four UPSs upgraded successfully to NMC v7.0.8.
This fixed the error message on the other firmware, although I haven't upgraded yet due to them needing to go offline to upgrade.
The HTTPS connection was still broken after this, but deleting the Web -> SSL Certificate and rebooting fixed this issue as well.
Many thanks for the help
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-18 12:58 PM
Were you able to upgrade the firmware? I updated the NMC but it still gives me the voltage error when I try to update the firmware.
Link copied. Please paste this link to share this article on your social media post.