Fairly old XS1300 F02 - Battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Fairly old XS1300 F02 - Battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
117
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:42 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
5
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:42 AM . Last Modified: ‎2024-03-27 12:46 AM

Fairly old XS1300 F02 - Battery?

I've got an XS1300 (BX1300G - SN B1029X48929). I think it's about 5 or 6 years old.  It's always worked flawlessly, and I've never replaced the battery.  A couple of weeks ago, the power flickered and the equipment lost power (I wasn't here, but I was told the power flickered for a split second).  The other day, the Back-UPS started screaming at me and had the F02 code.  I turned it off and unplugged the Back-UPS and everything plugged into it.  I eventually went back and plugged everything back in and it worked for a bit, then after an hour or two it threw the F02 code again. 

Tonight I plugged it in by itself and the battery went up to 80%.  I unplugged it and it shut down immediately.  I plugged it back in and then plugged a lamp in with an LED 11W bulb.  No issues.  I unplugged the UPS and it and the lamp shut down immediately, and after that shutdown, the battery level is showing 0%.

I'm leaning toward this just being a bad battery, but I don't want to buy a battery and then have to buy another UPS (especially since the new battery wouldn't fit the UPS that I'd be buying).

Is there a way to confirm that the issue is just the battery and not some other issue with the UPS?

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

It would be more cost effective for you to dispose of the unit locally.

Most transfer Stations / Dumps have a location for battery recycling and electronics disposal, usually at no cost.

Secret Squirrel

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:42 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:42 AM . Last Modified: ‎2024-03-27 12:46 AM

Hi Steve,

FO2  error is On battery output short, this means the battery is not able to output the power and there is something on the battery got short stopping it to output the power. I am sorry to say you need to replace the UPS rather then battery. You can contact technical support on 800-800-4272 for the recommended replacement. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:42 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:42 AM . Last Modified: ‎2024-03-27 12:46 AM

Hmm, interesting.  OK.

I performed several pull the plug tests last night and never got an F02. 

I left it plugged in all night but off so it could charge.  It showed a full charge this morning.  I plugged the lamp in and pulled the plug.  It immediately shutdown with an F02 again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

Hi Steve,

The F02 can be caused be a few things; a true Short at the Load, an old/weak internal battery or excessive load. I believe in your situation and considering the age of the battery, a simply battery replacement would suffice. That being said however, you take the chance that you only get a few more months out of the UPS before it fails completely. After 6yrs of service, the chances for a component failure increase exponentially. My advice would be to contact APC Sales and participate in their "Trade UPS" program. You will have the opportunity to trade in your old unit at a reduce price for the new replacement. You'll receive a NEW unit, NEW battery and a NEW 3yr warranty. A better investment!

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

Yeah, I had looked into that.  Sadly, it's cheaper to buy a new unit from the "mAjor online retailer" than it is to use the "Trade-UPS" program.  If I have to buy a new UPS, I would gladly send the old one with batteries back to APC if they cover shipping and they want it for recycling or whatever.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:46 AM

It would be more cost effective for you to dispose of the unit locally.

Most transfer Stations / Dumps have a location for battery recycling and electronics disposal, usually at no cost.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore