FAQ: What is the expected life of my APC UPS battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • FAQ: What is the expected life of my APC UPS battery?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
3
6431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

FAQ: What is the expected life of my APC UPS battery?

Most APC batteries should last three to five years. Below are some guidelines to ensure optimum life expectancy:

***Some APC Back UPS models may have a shorter battery life expectancy. Please reference the user's manual of your APC Back UPS to determine the exact battery life expectancy.

1. Make sure that you keep your APC UPS in a cool, dry location with plenty of ventilation. Ideally, the temperature where your UPS is kept should not exceed 75° F (24° C). Also, for ventilation purposes, leave roughly one to two inches on each side for proper airflow.

2. Only perform runtime calibrations on your UPS one or two times a year, if necessary. Some of our customers want to check their systems to verify that their runtime is sufficient. However, consistently performing these calibrations can significantly decrease the life expectancy of your APC battery.

3. Do not store APC batteries for extended periods of time. New batteries can be stored for 6 to 12 months. After this period, the battery should be used or it will lose a great deal of its charge. It is not advisable to store batteries that have already been in use.

4. Do not exceed 80 percent of a UPS unit’s rated capacity due to the reduction in run time. When you increase your load, your runtime lessens. In the event of a power failure, a UPS loaded to full capacity will drain and discharge it’s battery quickly and will lessen the life expectancy.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
6431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

I just bought my BE325R Surge Protector/Battery about a year ago. Tonight, when I got home the alarm was sounding on it. I turned it off and then on again. It hasn't gone off since. Does this mean I need to replace the battery? Shouldn't it have lasted longer than this?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
6432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

II'd like to add a few things from what I know and experience.

WildWatt wrote:
Most APC batteries should last three to five years. Below are some guidelines to ensure optimum life expectancy:

***Some APC Back UPS models may have a shorter battery life expectancy. Please reference the user's manual of your APC Back UPS to determine the exact battery life expectancy.

1. Make sure that you keep your APC UPS in a cool, dry location with plenty of ventilation. Ideally, the temperature where your UPS is kept should not exceed 75° F (24° C). Also, for ventilation purposes, leave roughly one to two inches on each side for proper airflow.

2. Only perform runtime calibrations on your UPS one or two times a year, if necessary. Some of our customers want to check their systems to verify that their runtime is sufficient. However, consistently performing these calibrations can significantly decrease the life expectancy of your APC battery.

3. Do not store APC batteries for extended periods of time. New batteries can be stored for 6 to 12 months. After this period, the battery should be used or it will lose a great deal of its charge. It is not advisable to store batteries that have already been in use.
SLA batteries can be stored for a few years with little loss of performance if they're topped off every 3-6 months. As long as they're properly topped off, they will hardly degrade. You need to charge them before they fall below 60% capacity or they will permanently degrade in capacity. About 12mo at 25C, less at higher temp.
http://img262.imageshack.us/img262/8952/slastoragedb6.png
From 12v 17Ah CSB battery engineering datasheet (two of them makes an RBC7)

Batteries in service will degrade from electrode corrosion from being placed on 13.8v/pack float voltage and accelerated deterioration from higher temperature inside the cabinet.

SLA in extended storage degrade from sulfation.

Best life from temporarily decommissioned UPS can be obtained from leaving them disconnected from power, but allowed to charge on an appliance timer in storage area for an hour or so a week to automatically replenish the battery.
4. Do not exceed 80 percent of a UPS unit’s rated capacity due to the reduction in run time. When you increase your load, your runtime lessens. In the event of a power failure, a UPS loaded to full capacity will drain and discharge it’s battery quickly and will lessen the life expectancy.
I believe that heavy loads don't actually reduce the actual degradation speed of battery, but battery simply simply loses their maximum load sustaining ability as they increase in their internal impedance. There's also a trend in consumer grade UPS to mate a larger inverter with a smaller battery.

I recommend around 50% load or less for newer consumer grade UPS. A 450VA UPS from 1992, BK450 came with a 12Ah battery, but these days, you'll find 750VA units with a smaller battery, so the battery is actually pushed harder.

You can't change the rate of actual degradation, but if you don't push the battery pack hard and you leave more than enough runtime, you increase the service life until the performance reaches below expectation, for example if you need 200W for 5minute, getting a UPS that can supply 200W for 10 minutes will remain serviceable until it can only maintain 5 minutes where a unit that can only do 6 minutes with new batteries will fall below 5 minutes mark far sooner.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
6432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

I just bought my BE325R Surge Protector/Battery about a year ago. Tonight, when I got home the alarm was sounding on it. I turned it off and then on again. It hasn't gone off since. Does this mean I need to replace the battery? Shouldn't it have lasted longer than this?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:39 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
6432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:39 PM . Last Modified: ‎2024-03-26 01:09 AM

Chances are it's indicating a battery disconnect. I would double and triple check the battery connection on this UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of