ES 550 constant bip and computer shut down

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • ES 550 constant bip and computer shut down
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
9
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

ES 550 constant bip and computer shut down

Hello,

I own an APC BACKUPS 550 and i have an issue that happened two or three time since i bought it 2 years ago.

So i was coding and my computer just shut down. The APC emitted a constant bip. I had to rearm it and restart my computer. There was no problem like no electricity problems. But i don't really know what this means. Could someone help me ? I own this for my personal use and it always worked like a charm.

What should i look for to see if the APC is still working ? What's that beeping ? There's 3 stuff that can cause constant beeping in the manual but i don't know how to differenciate it. 

I try to unplug the APC and the computer was still on so i think it's still working but i don't understand what is happening with that constant bip.

TL;DR

- Out of the blue. Computer shuts down. Constant bip.

- Rearm. It's fine.

- Tested to unplug the APC from the wall. 

- Computer is on. Bips from the APC (normal ones when there's a problem with power)

Sorry for my english 😞 and thanks in advance for your help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 550
  • apc
  • es
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

Hello Antoine,

I have a similar problem with my ES 550. Just of the warranty of 3 years expired, it started to do a bip sound. And I don't mean just a bip-bip-bip, but one long biiiiiiiiiiiiiiiiiiiiiiip.

I disconnected it from all devices and I still have the same problem: As soon as I turn on the battery support I get that sound. I also connected it to a PC and installed the "PowerChute Personal Edition v3.0.2" which I downloaded from APC. But I didn't seen any problems there.

The interesting thing is: If I take the ES 550 to another electrical socket it doesn't do the sound (didn't try to connect any device to it). If I take it to another socket I get it again. If I take it back to the socket which was okay, it doesn't give me the bip again. So I can reproduce it, but I don't know the reason / the cause for it.

First I thought that maybe the battery is too old. But the PowerChute didn't show anything. And it also wouldn't explain why I get that sound on some sockets while I don't get it on some other ones. Somehow mysterious...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

It's possible that your Back-UPS ES 550 is being overloaded. I don't think it would cut off power to attached devices in the face of an overload unless there is a power problem and the inverter is running from battery.

An inexpensive inline metering device (something like the P3 Kill-A-Watt, or a similar device) can tell you exactly how much electricity your computer consumes. Easiest thing to do would be to plug the Back-UPS into the measurement device and see what everything is drawing. To get the worst-case figure, do something that holds the CPU usage at 100% for a little while.

Although they're sold as being suitable for computer use, all the various "plugstrip" style APC UPS products really a bit light for the job. It's best to keep a UPS loaded to about 50% of its capacity rating at any given time.

If checking with a power meter rules out an overload condition, the battery could have failed or the unit itself may have a problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

Hello.

Thank your or your answer. Well it can't be the computer since it's plugged in since the start so.... But i tried anyway since i ddon't have a measure device

I have done a really simple test since the problem happened again. 

I hooked up the APC on another wall alone. With NOTHING on it. Two hours after. It started to do the constant bip again.

Weird thing, there's no light with the beeping. Which is OVERLOAD in the manual. Overload with nothing ? i thought APC lasted longer than 2 years 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

I do not completely understand what you are saying about the constant beeping sound and exactly when it happened during your test.

It is possible that the unit has failed, or the battery is no longer any good. How much life you get from the battery varies depending upon the quality of your electrical service.

Several things can cause the constant beeping sound:

1. An overload.

2. A bad battery.

3. An internal fault in the UPS.

4. Low battery.

The LED light flashes when the unit is running on battery or performing a self test. It may be "latched" off when the fault occurs.

Maybe there are other things that can trigger the constant beeping. I do not work for APC or Schneider Electric, and as a result I do not know everything about how they programmed the microcontroller in your UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:01 AM . Last Modified: ‎2024-03-27 02:00 AM

Hello,

I plugged the APC alone (with nothing plugged on it) and 2 hours later, it did the constant bip. I don't think there is other things that the thing you mention (because that's exactly what is in the manuel).

Is there a way to test the battery ? Other than plug something on it then unplug the APC ? (a real test i mean) ?

Thanks again for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

Hi,

You can test the battery with a DC volt meter. When not connected to the UPS the voltage should read 13.5 for a good battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

Ok thanks. I need to find one. Mine was lost when moving.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

On 1/9/2016 6:32 AM, William said:

It's best to keep a UPS loaded to about 50% of its capacity rating at any given time.

What happens, if the load goes up to, let´s say, 70% or even 80%? Will the UPS become unstable or will it shut down earlier than expected?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

On 1/21/2016 4:34 AM, Malte said:

What happens, if the load goes up to, let´s say, 70% or even 80%? Will the UPS become unstable or will it shut down earlier than expected?

It may shut down sooner than expected due to faster battery exhaustion. This is especially true if the batteries are no longer new. Batteries will wear out faster under the heavier load, and may have to be replaced more often.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:02 AM . Last Modified: ‎2024-03-27 02:00 AM

Hello Antoine,

I have a similar problem with my ES 550. Just of the warranty of 3 years expired, it started to do a bip sound. And I don't mean just a bip-bip-bip, but one long biiiiiiiiiiiiiiiiiiiiiiip.

I disconnected it from all devices and I still have the same problem: As soon as I turn on the battery support I get that sound. I also connected it to a PC and installed the "PowerChute Personal Edition v3.0.2" which I downloaded from APC. But I didn't seen any problems there.

The interesting thing is: If I take the ES 550 to another electrical socket it doesn't do the sound (didn't try to connect any device to it). If I take it to another socket I get it again. If I take it back to the socket which was okay, it doesn't give me the bip again. So I can reproduce it, but I don't know the reason / the cause for it.

First I thought that maybe the battery is too old. But the PowerChute didn't show anything. And it also wouldn't explain why I get that sound on some sockets while I don't get it on some other ones. Somehow mysterious...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of