Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82522members
350123posts

Does the BN1500M2 UPS auto restart after complete battery loss shutdown?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

XM-305871057
Cadet
0 Likes
1
173

Does the BN1500M2 UPS auto restart after complete battery loss shutdown?

My client has been using cyber power UPS units for an IP camera system outdoor enclosure.  I am looking at the UPS listed below as an alternative to these as they do not auto restart upon an extended outage based shutdown (when the batteries are completely drained).   This is causing unnecessary service calls at the client's expense. 

 

Also the website states it uses USB for connection to a computer for UPS configuration, but all I see are the two surge RJ-45 Jacks, and one RJ-45 jack labeled Data port.  Is it a serial rj45 USB port or something?  I wouldn't expect network connectivity at this price range.

 

https://www.apc.com/shop/us/en/products/APC-Back-UPS-Pro-1500VA-120V-AVR-LCD-2-USB-charging-ports-10...

 

Thanks in advance for doing my job.

 

image.png

Tags (1)
1 Reply 1
RichA
Crewman
Crewman
0 Likes
0
109

Re: Does the BN1500M2 UPS auto restart after complete battery loss shutdown?

The connector labeled "Data port" is actually USB.  The unit comes with a special cable, RJ45 to USB,  to plug into a computer.

 