Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Does Back-UPS compensate for low input voltage?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Does Back-UPS compensate for low input voltage?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

0 Likes
4
7912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

Does Back-UPS compensate for low input voltage?

Hi, I have a Back-UPS BE850M2

  1. My electric supplier has intermittent brown-outs. On hot days my house voltage ranges from 92 to 100v. Does my UPS protect against low voltage? The manual says it protects surges but I don't see low voltage?  Research on this forum says that it's model-specific.  Does my model offer low voltage regulation?
  2. I have a brand new All-in-One computer with an SSD, I don't want low voltage to damage it. I can't find any specs about acceptable voltage range for my model.  However it can run on the UPS battery for a couple hours (according to the PowerChute s/w).  The best s/w setting for battery take-over due to low voltage is 96v which seems too low to me.   Is there any way to set the battery to take over at 105v?
    Thanks.
Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

0 Likes
0
7911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

Thank you.  My UPS is still going strong but I'll get one with AVR when I replace it. 

I had mistakenly thought that all UPSes have that feature, not sure where I got that idea.

I appreciate your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

0 Likes
0
7911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

Hello,

On 7/15/2019 12:37 PM, James said:

Does my UPS protect against low voltage? 

Yes. If the voltage drops below the pre set low voltage setting the UPS will switch to battery power to protect the attached equipment. The typical brownout transfer is 92 Vac.

The User's Guide list the settings as

 Green LOW 88 Vac to 142 Vac Use this setting with equipment that is less sensitive to fluctuations in voltage or waveform distortions.

Red MEDIUM 92 Vac to 139 Vac Factory default setting. Use this setting under normal conditions.

Amber HIGH 96 Vac to 136 Vac Use this setting when connected equipment is sensitive to voltage and waveform fluctuations.

The User's Guide is available at this link https://www.apc.com/salestools/AHUG-A52BFR/AHUG-A52BFR_R3_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

0 Likes
0
7911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

Thanks for the reply.

I realize that I wasn't clear in my question.  What I was trying to ask was if the UPS routinely leveled the power during under-voltages, prior to reaching the 96v threshold.  For example, if the AC input dropped to 100v, would the UPS boost it to, say, 110v to the computer.  Not going on full battery backup, but just raising the low voltage up to a more normal value. 

From researching this, that feature is available in some APC UPSes.  It's called Automatic Voltage Regulation. From elsewhere on the APC website: "With AVR Technology, instead of going to battery during high or low input voltages, the unit will increase (BOOST) or reduce (TRIM) the voltage to a safe operating range. This is achieved by re-routing the input voltage through the internal Automatic Voltage Regulating transformer, all without running off of the internal battery."

That's what I was hoping mine would do, but apparently it does not.  At least I can't find anything about my model that says it has AVR. 

Since I can't find the minimum operating voltage for my computer, I'd feel better not chancing going down to 96v.  Even if the computer is rated okay below that, I'd prefer not to push the limit. My computer is only a couple weeks old so I'm trying to be particularly protective.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

0 Likes
0
7911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

Hi,

That unit does not have AVR. If you would like AVR with a Back-UPS you should look at the Back-UPS Pro line.

Here is a link to a Back-UPS Pro 1000 https://www.apc.com/shop/us/en/products/Back-UPS-PRO-BR-1000VA-SineWave-10-Outlets-2-USB-Charging-Po...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

0 Likes
0
7912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 AM . Last Modified: ‎2024-03-26 03:41 AM

Thank you.  My UPS is still going strong but I'll get one with AVR when I replace it. 

I had mistakenly thought that all UPSes have that feature, not sure where I got that idea.

I appreciate your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore