Does ASUS "Anti Surge Support" play well with APC Backups ?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Does ASUS "Anti Surge Support" play well with APC Backups ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
111
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
3
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

Does ASUS "Anti Surge Support" play well with APC Backups ?

Hi,

A customer with a Backups 500ES (battery replaced 1/2016) and an ASUS P8B75/M-CSM  motherboard had power wink out several times for maybe 15 seconds max the other day. This all happened within about a two minute period. The PC did not stay powered on as expected. After the power events, the PC would the not boot into Windows O/S, but  only to the UEFI login prompt (UEFI is password protected). I had them press the reset button several times and then it finally booted into Windows, and checkdsk ran automatically a couple times, then all was fine and Windows booted.

I have that PC at my office for a Windows upgrade. In the UEFI, in the Monitor tab (ie. fan speed temps, etc), I see that there's a setting called "Anti Surge Support" that's enabled. The description says, "If enabled, system will have uvp or ovp protection."

Do you have any knowledge of this setting interfering with, or reacting adversely with your Backups 500ES product?

Thank you for your assistance.

Regards . . .

P.S. There's something wrong with spaces between words in this thread editor.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

Asus's claims are likely nothing more than marketing. Any specialized protections on the board would be ready to operate at all times, and not toggled on or off through some kind of setup utility. I suspect that if the option in setup does anything, all it would do is somehow interrupt the currently running program to provide an alert indicating that the computer's power supply may be malfunctioning. By that point it may already be too late.

Sudden shutdowns can point to a faulty battery. Even though the battery is only a year old at this point, I'd recommend testing it with a "dummy" load. Incandescent lamps work well for this. It is also possible that the UPS has developed a fault.

Another common problem that results in sudden shutdowns comes from computer power supplies that are sensitive to the incoming AC waveform. Potentially affected power supplies usually indicate the presence of an active power factor correction circuit. Some of these circuits are sensitive to the incoming AC power waveform. On utility power this should be a smooth sine wave. When the UPS switches to battery power and takes over in the face of a power outage, its inverter outputs a "modified" sine wave. This is actually a square wave with periodic drops to a zero output level.

If this is the problem you're having, only one of two things will cure it: changing to a UPS with a true sine wave output or changing out the computer's power supply. APC's Smart-UPS 750, 1000, 1500 and larger units all have a true sine wave output.

The "misisng spaces" issue is caused by certain web browsers, particularly those basing on a Webkit or Chrome/Blink foundation.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

Asus's claims are likely nothing more than marketing. Any specialized protections on the board would be ready to operate at all times, and not toggled on or off through some kind of setup utility. I suspect that if the option in setup does anything, all it would do is somehow interrupt the currently running program to provide an alert indicating that the computer's power supply may be malfunctioning. By that point it may already be too late.

Sudden shutdowns can point to a faulty battery. Even though the battery is only a year old at this point, I'd recommend testing it with a "dummy" load. Incandescent lamps work well for this. It is also possible that the UPS has developed a fault.

Another common problem that results in sudden shutdowns comes from computer power supplies that are sensitive to the incoming AC waveform. Potentially affected power supplies usually indicate the presence of an active power factor correction circuit. Some of these circuits are sensitive to the incoming AC power waveform. On utility power this should be a smooth sine wave. When the UPS switches to battery power and takes over in the face of a power outage, its inverter outputs a "modified" sine wave. This is actually a square wave with periodic drops to a zero output level.

If this is the problem you're having, only one of two things will cure it: changing to a UPS with a true sine wave output or changing out the computer's power supply. APC's Smart-UPS 750, 1000, 1500 and larger units all have a true sine wave output.

The "misisng spaces" issue is caused by certain web browsers, particularly those basing on a Webkit or Chrome/Blink foundation.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

You could say the missing spaces are because those browsers insert non-breaking spaces sometimes, or you could say it's because the forum software doesn't convert them to true spaces, or you could say it's because APC's custom webfont has no glyph for a non-breaking space.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

0 Likes
0
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:23 AM . Last Modified: ‎2024-03-27 01:02 AM

Thanks for the options William. I've marked your reply as answer.

I'm going to disable that switch, and (not always recommended) pull the AC plug to try to simulate the power outages. I'd rather use the circuit breaker, but that would disrupt other equipment there. Likewise, I'll try the same with that feature enabled. Let you all know what shakes. Although not pure sine, I have a new Back-UPS 700 (BN700NC) on the shelf and cna use that for some comparisions.

Btw voidstar, thanks for feedback on missing typed spaces. I'm doing this post in Firefox. See what happens when I save.

Regards . . .

P.S. After saving, all looks good in Firefox with spaces now. Must have been a Google Chrome issue.

P.S. Now I'm, looking at this in Google Chrome, and everything looks good here too today. Who knows what was up. No to worry.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore