Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Different Battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Different Battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
106
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

0 Likes
7
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

Different Battery

Hello,

I have a Back-UPS CS 350. I'm currently working on a project that has limited space and would like to know if i can change the size of the battery that is compatible with above mentioned UPS.

DEFAULT BATTTERY: CSB; GP 1272 F2; 12V; 7.2Ah

BATTERY IN QUESTION: YUASA; NP1.2-12: 12V; 1.2Ah

Any help would be greatly appreciated. Thank you.

OverklocK

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

overklock wrote:
Hello,

I have a Back-UPS CS 350. I'm currently working on a project that has limited space and would like to know if i can change the size of the battery that is compatible with above mentioned UPS.

DEFAULT BATTTERY: CSB; GP 1272 F2; 12V; 7.2Ah

BATTERY IN QUESTION: YUASA; NP1.2-12: 12V; 1.2Ah

Any help would be greatly appreciated. Thank you.

OverklocK
The difference is huge. It's probably a bad idea. The UPS itself draws some power under no load while running on battery and that alone is quite a bit of burden for a 1.2Ah battery. Add some load and expect the runtime to be significantly less than simple (1.2/7.2). Battery's capacity is variable depending on relative load unlike a tank of gas.

The UPS is designed with charging current for a 7.2Ah cell in mind, so the charging current maybe excessive and cause a 1.2Ah pack to vent/overheat. Even if it doesn't get this bad, SLA batteries don't like to be fast charged and if the charging current exceeds the permissible current as written on the battery case, don't expect your batteries to live long.

Message was edited by: KVAr

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

Hello,

While YUASA is a brand that's sometimes used for APC products, the VA/hr. is going to throw off your runtime, and probably not even provide the necessary charge for the UPS. I'm sure if KVar is around these boards he can shed more light since it seems he has to have more of a plethora of knowledge of the use of non-APC batteries in APC systems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

0 Likes
0
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 PM . Last Modified: ‎2024-03-26 01:05 AM

overklock wrote:
Hello,

I have a Back-UPS CS 350. I'm currently working on a project that has limited space and would like to know if i can change the size of the battery that is compatible with above mentioned UPS.

DEFAULT BATTTERY: CSB; GP 1272 F2; 12V; 7.2Ah

BATTERY IN QUESTION: YUASA; NP1.2-12: 12V; 1.2Ah

Any help would be greatly appreciated. Thank you.

OverklocK
The difference is huge. It's probably a bad idea. The UPS itself draws some power under no load while running on battery and that alone is quite a bit of burden for a 1.2Ah battery. Add some load and expect the runtime to be significantly less than simple (1.2/7.2). Battery's capacity is variable depending on relative load unlike a tank of gas.

The UPS is designed with charging current for a 7.2Ah cell in mind, so the charging current maybe excessive and cause a 1.2Ah pack to vent/overheat. Even if it doesn't get this bad, SLA batteries don't like to be fast charged and if the charging current exceeds the permissible current as written on the battery case, don't expect your batteries to live long.

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

sorry it's been so long since i've logged on but none-the-less, thank you so much for your response KVAr...it's precisely the answer i was looking for...you've saved me from blowing up my dog who loves laying near the apc because of it's warmth, lol...so if that's out of the question, any recomendations you can give me on the smallest APC unit that can still keep a car alarm running, and 120V air pump, a few flourescent 15" tube lights (12V), and a bunch of 5v LED's?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

The size would be a matter of how long you want to "keep running"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

essentially, it would only need to run about 10min...any more than that would be a bonus-=]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

new question

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 PM . Last Modified: ‎2024-03-26 01:04 AM

overklock wrote:
new question
It might, it might not. Depends on the characteristic of the battery and your loads.

If we assume your total load is 48W and draws, 4A, a 4Ah battery would be loaded at 4A, which would be represented as "1C rate". If it's a 2Ah battery, it would be 2C rate.

The higher the relative load, the lesser the capacity that can be used. Name plate capacity is rated at 1/20C. So, for a 1.2Ah battery pack, it's 0.06A. At 4A or ~3.5C you wouldn't get anywhere near the rated capacity of 1.2Ah. You'll have to study the characteristics of the battery pack and the actual combined power draw.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore