Current draw of Smart UPS 1400 from wall

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Current draw of Smart UPS 1400 from wall
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
4
2095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

Current draw of Smart UPS 1400 from wall

I'm looking into getting a used Smart UPS 1400, and I'm somewhat current-limited in my new place, so I need to get a rough idea of how many amps this UPS pulls.

My equipment draws around 3A. When the battery is fully charged, how many amps will the UPS draw? What about after a 10-20 minute spell without power, and it has to recharge the battery?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
0
2096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

Is it on "max" when you got the current? My energy meter cycles through volts, amps, max amps, watts, and max watts.

Could you run something off the wall and then through the UPS (powered from wall) to see what the difference in amperage is? I'm hoping it doesn't jump up too drastically.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
0
2096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

Well, I'm not sure what exactly is going on. I checked the Kill-A-Watt meter against two lamps with a known wattage and got the results I was expecting.
-------------------------------------------------------------------------------
Lamp 1) 60 watt
Kill-A-Watt readings: Volt: 118.9, Amp: .47, Watt: 57

Lamp 2) 150 watt
Kill-A-Watt readings: Volt: 118.7, Amp: 1.22, Watt: 145
-------------------------------------------------------------------------------

Both of these add up correctly, now plug the Smart-UPS back in...

Test 1) Sitting idle, not charging, no load
Kill-A-Watt readings: Volt: 119.4, Amp: .82, Watt: 20

Test 2) Not charging, 150 watt lamp load
Kill-A-Watt readings: Volt: 118.6, Amp: 1.63, Watt: 165

Test 3) Charging and 150 watt lamp load
Kill-A-Watt readings: Volt: 118.7, Amp: 2.48, Watt: 270

Test 4) Charging, no load
Kill-A-Watt readings: Volt: 118.9, Amp: 1.13, Watt: 82

In none of the cases does the Kill-A-Watt 'Volts x Amps = Watts' formula add up with the Smart-UPS 1500 as it should. This is perplexing indeed, if anyone knows what the heck is going on, please let me know.

Stew.

Lowboy: The readings are real time, there isn't a max screen. Good thought though, the mystery deepens...

Message was edited by: Stew-2

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
0
2096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

My Smart-UPS 1500 is measuring about .89amp/30watt while charging the battery or about 11watts not charging.

I've contacted support for my Kill-A-Watt meter because at 119.1v, something isn't adding up right. .89amps would be about 106 watts, not 30.

But at least that gives you a ballpark number

Take care,
Stew

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

Is it on "max" when you got the current? My energy meter cycles through volts, amps, max amps, watts, and max watts.

Could you run something off the wall and then through the UPS (powered from wall) to see what the difference in amperage is? I'm hoping it doesn't jump up too drastically.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

Well, I'm not sure what exactly is going on. I checked the Kill-A-Watt meter against two lamps with a known wattage and got the results I was expecting.
-------------------------------------------------------------------------------
Lamp 1) 60 watt
Kill-A-Watt readings: Volt: 118.9, Amp: .47, Watt: 57

Lamp 2) 150 watt
Kill-A-Watt readings: Volt: 118.7, Amp: 1.22, Watt: 145
-------------------------------------------------------------------------------

Both of these add up correctly, now plug the Smart-UPS back in...

Test 1) Sitting idle, not charging, no load
Kill-A-Watt readings: Volt: 119.4, Amp: .82, Watt: 20

Test 2) Not charging, 150 watt lamp load
Kill-A-Watt readings: Volt: 118.6, Amp: 1.63, Watt: 165

Test 3) Charging and 150 watt lamp load
Kill-A-Watt readings: Volt: 118.7, Amp: 2.48, Watt: 270

Test 4) Charging, no load
Kill-A-Watt readings: Volt: 118.9, Amp: 1.13, Watt: 82

In none of the cases does the Kill-A-Watt 'Volts x Amps = Watts' formula add up with the Smart-UPS 1500 as it should. This is perplexing indeed, if anyone knows what the heck is going on, please let me know.

Stew.

Lowboy: The readings are real time, there isn't a max screen. Good thought though, the mystery deepens...

Message was edited by: Stew-2

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

0 Likes
0
2096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:08 AM . Last Modified: ‎2024-03-22 04:11 AM

Odd indeed! Anyway, it gives me an idea of what to expect, thanks for doing that!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore