Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Posted: 2021-06-28 07:16 AM . Last Modified: 2024-03-26 10:37 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:16 AM . Last Modified: 2024-03-26 10:37 PM
I have a 1200a jump starter kit/pack with an AC outlet on it. I was wondering if it would be okay to plug the APC to the jump starter only when the power goes out for more power/runtime. Both are made by Schneider, if that matters.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:16 AM . Last Modified: 2024-03-26 10:37 PM
Hi Uzuki,
The 1200a "jump starter pack" is most likely a modified sine wave output, rather than a pure sinusoidal wave form. Essentially what this means is that although the modified sine wave is acceptable to most equipment, the UPS will likely see the output of the "jump starter pack" as being unacceptable and will instead remain on it's own internal battery power. This is due to the nature of the UPS and it's ability to monitor utility power for various types of power anomalies.
Secret Squirrel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:16 AM . Last Modified: 2024-03-26 10:37 PM
Hi Uzuki,
The 1200a "jump starter pack" is most likely a modified sine wave output, rather than a pure sinusoidal wave form. Essentially what this means is that although the modified sine wave is acceptable to most equipment, the UPS will likely see the output of the "jump starter pack" as being unacceptable and will instead remain on it's own internal battery power. This is due to the nature of the UPS and it's ability to monitor utility power for various types of power anomalies.