Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Computer still shuts down

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Computer still shuts down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:28 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
8
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:28 AM . Last Modified: ‎2024-03-21 11:08 PM

Computer still shuts down

I have recently purchased two APC Back-UPS ES systems, a 550 and 750. Both are fully charged and seem to be working correctly however they are not always preventing my computer from shutting down if there is a momentary power issue. At first I though the problem was the UPS 750 so I returned it for another one but still had the same issue.
The PC I seem to be having the most problem with is a one year old Dell desktop, Studio XPS 9000 . Should a power outage occur, the UPS alarm sounds but the PC immediately cuts out and reboots; however not always. This intermittent problem seems to happen with either the 550 or the 750. In both cases the only other item plugged in is an external hard drive by Western Digital that does not draw very much power at all.
Both units are being used stand alone, in other words I only have the AC line plugged into the UPS, no special software is installed and there is no other communications between the UPS and PC.
Any ideas as to what is causing the problem would be appreciated.
Thanks,
John

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:07 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:07 PM

I myself got confused as well with the post above.

Let us set this straight. What UPS are you using? Where is the PC and Hard Drive connected and on what receptacles? Let us try to do the following steps:

1. Turn the UPS ON as well as the load attached to it.
2. Make sure that the UPS has been charged to 100%.
3. Unplug the UPS from the power source and let it run On Battery.
4. Do no do anything with the Hard Drive and PC, kindly observe what will happen to them once the UPS is running On Battery.
5. Let me know what would happen on the UPS and the load.
6. When you re-apply power to the UPS, observe what would happen to the load and the UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:28 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:28 AM . Last Modified: ‎2024-03-21 11:08 PM

I can't tell if the external hard drive is cutting out as well. The monitors are plugged into a one of the UPS systems and the PC into the other. These power interruptions are very small, my guess is a second or less, so while I lose the display of the monitor I can not tell if it is actually losing power. If I unplug the UPS for the monitors they stay on. Both UPS systems are on the same fuse circuit. My main concern is protecting the PC and not losing my work.
Not sure this is helping. Where to look next? Thanks for your help,
John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

Does the external hard drive reboots as well or is it just the XPS PC? How about your Monitor, does it reboot itself as well?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

Alright, so it's the XPS alone that is attached on this UPS. I assume that you it installed on the Battery side of the UPS. When you unplug the UPS and let it run on battery, does the XPS turns off and starts back up again or does it remain on off state? Is there a possibility to use/add a different load on the UPS to see if that load would drop or reboot as well?

If the UPS is on battery and the XPS has rebooted already, does the XPS stays on? If the PC reboots and stays on while it is on battery, a reason why it does this is due to the transfer time.

Here are some APC Knowledge Base Articles that I hope could help you out.

Article Link: [Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.|http://nam-en.apc.com/app/answers/detail/a_id/20/kw/drop%20load]

Article Link: [Computers containing PFC (Power Factor Corrected) power supplies and their use with Back-UPS or Smart-UPS SC UPS.|http://nam-en.apc.com/app/answers/detail/a_id/8883/kw/drop%20load]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

This is getting more confusing.
My PC and external hard drive are connected to the battery portion of the 550 UPS. To test, I saved my work and then rebooted the computer.
With the computer rebooted I unpluged the UPS, sure enough the PC cut out. It appeared that the HD continued but the light soon went out, mind you I don't believe it lost power as this is connected via USB to the PC, with the PC off the HD shuts off.
The alarm continued to sound on the ES 550 so I plugged in a 60 watt utility light into the unit to see if it was functioning on battery and it was. Now for the very odd thing, when I turned on the light, the computer restarted.....please note the UPS was still unplugged and the alarm was sounding.
Thank you for the articles however I am not sure if the powers supply in the PC is PFC and if it was should the 550 not provide enough power?
I checked the event view of the PC, Windows 7, and it showed a critical error, event 41, task 63, source Kernel-power.
I am a little stumped.
I could try this with the ES 750 but my guess is I will get the same result?
Any ideas?
Thanks again, John

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

Sorry for any confusion.
The UPS, is an ES-550 purchased a few weeks ago; however I also have an ES-750 that I get the same results. Both are fully charged.
My PC and external hard drive are plugged into the battery backed up side of the ES-550. The external drive is connected to the PC via USB. My concern in determining if the external drive is being affected by the UPS is that it will be affected by the USB connection to the PC. When the PC shuts down it will turn off the external drive.
Thus I did these test with a 60 watt light plugged in the battery backed up side of the UPS.
When power is removed from the UPS, the PC shuts down but the light stays on. When power is restored to the UPS the computer reboots.
What I experienced earlier is when the UPS was unplugged and the PC shut off, when I plugged in the light into the UPS the computer rebooted, which is what I found very odd. It was like the load to the light caused the PC to reboot.
I am starting to suspect a problem with the power supply of the PC but it seems to be running fine.
Please let me know if I have answered your questions.
Thank you

Message was edited by: jlemme

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

0 Likes
0
2841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:08 PM

I think I may have found others with the same problem,
check this thread,
https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/bd-p/home-office-forum

What do you think? Is the issue the pure sine wave?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:07 PM

0 Likes
0
2841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:07 PM

jlemme wrote:
When power is removed from the UPS, the PC shuts down but the light stays on. When power is restored to the UPS the computer reboots.
What I experienced earlier is when the UPS was unplugged and the PC shut off, when I plugged in the light into the UPS the computer rebooted, which is what I found very odd. It was like the load to the light caused the PC to reboot.
You've said that when you removed the power from the UPS, the PC shuts down. Was it an immediate shutdown/ drop load or was it a graceful shutdown? Normally, the PC would reboot once power is restored is if you have it configured on the BIOS settings.

Some issues that I have seen when it comes to sine wave are those customers who are experiencing drop load situations when the BackUPS goes to battery. The equipment that they have does not like the waveform that is being supplied by the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:07 PM

0 Likes
0
2842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:29 AM . Last Modified: ‎2024-03-21 11:07 PM

I myself got confused as well with the post above.

Let us set this straight. What UPS are you using? Where is the PC and Hard Drive connected and on what receptacles? Let us try to do the following steps:

1. Turn the UPS ON as well as the load attached to it.
2. Make sure that the UPS has been charged to 100%.
3. Unplug the UPS from the power source and let it run On Battery.
4. Do no do anything with the Hard Drive and PC, kindly observe what will happen to them once the UPS is running On Battery.
5. Let me know what would happen on the UPS and the load.
6. When you re-apply power to the UPS, observe what would happen to the load and the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore