Chirping of BACK-UPS LS 700

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Chirping of BACK-UPS LS 700
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
8
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

Chirping of BACK-UPS LS 700

The last 2 weeks the unit has been "chirping" twice randomly while flashing the replace battery red light. It might go 8 to 10 hours without a sound and then it might do it 3 times in the next hour. I have "on line chatted" with APC and called tech support but get people who don't know anything. They want you to upgrade or buy a battery. On line chat thought it was the unit trying to regulate voltage and wanted me to lower the sensitivity. Can't do that with this unit. Right? Tech support said software won't work on my operating system. I have mac 10.4.9. He said it would only work on 10.4.1. Performed the battery test by holding down power button and everything performed OK. If battery was bad wouldn't the red light stay lit? Help Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

The last 2 weeks the unit has been "chirping" twice randomly while flashing the replace battery red light. It might go 8 to 10 hours without a sound and then it might do it 3 times in the next hour. I have "on line chatted" with APC and called tech support but get people who don't know anything. They want you to upgrade or buy a battery. On line chat thought it was the unit trying to regulate voltage and wanted me to lower the sensitivity. Can't do that with this unit. Right? Tech support said software won't work on my operating system. I have mac 10.4.9. He said it would only work on 10.4.1. Performed the battery test by holding down power button and everything performed OK. If battery was bad wouldn't the red light stay lit? Help Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

APC told me it was out of warranty. PB0336324463

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

The audible tone for Replace Battery is that the UPS beeps for one minute every five hours.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

Have you ever replaced the battery inside the UPS? Chirping sound usually indicates a bad battery within the unit.

That serial number would be out of warranty, but you can purchase a new battery, RBC17, or trade in the UPS for a brand new unit via our TradeUPS program.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

It's seems to me, that batteries are not connected properly, or batteries need replacement. Also maybe unit has fault to properly charge the batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

Wouldn't the unit react systematically instead of randomly? It has not chirped in about four hours.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

I have heard the unit "beep" when the electricity goes off, This is two quiet chirps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

Assuming it was in service, with a 2003 date, the battery is getting near the end of life.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 PM . Last Modified: ‎2024-03-26 01:40 AM

The last 2 weeks the unit has been "chirping" twice randomly while flashing the replace battery red light. It might go 8 to 10 hours without a sound and then it might do it 3 times in the next hour. I have "on line chatted" with APC and called tech support but get people who don't know anything. They want you to upgrade or buy a battery. On line chat thought it was the unit trying to regulate voltage and wanted me to lower the sensitivity. Can't do that with this unit. Right? Tech support said software won't work on my operating system. I have mac 10.4.9. He said it would only work on 10.4.1. Performed the battery test by holding down power button and everything performed OK. If battery was bad wouldn't the red light stay lit? Help Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore