Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84724members
354137posts

Check of the UPS runtime

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
farmaceits_apc
Cadet
0 Likes
2
115

Check of the UPS runtime

This was originally posted on APC forums on 9/18/2007


I would like to check of the UPS BackUPS CS 500 (BK500EI) runtime by halfload. If it is correct to check runtime with 250W light bulb, not with 150W light bulb? I think that 250W (PF=1) for light bulb is the same 150W (PF=0.7) for computer.

Tags (3)

Accepted Solutions
KVAr_apc
Captain
Captain
0 Likes
0
115

Re: Check of the UPS runtime

This was originally posted on APC forums on 9/21/2007


Power factor doesn't matter for the most part for runtime test. You just want the load to simulate what your expected backup load is using in watts.

If you're doing a general UPS calibration, charge 24 hours, then use resistive load (like light bulbs) with 30-50% the wattage rating of UPS and let it run until it shuts off on its own.

See Answer In Context

2 Replies 2
dirtfoot_apc
Lt. Commander
Lt. Commander
0 Likes
0
115

Re: Check of the UPS runtime

This was originally posted on APC forums on 9/18/2007


A runtime chart is available for your UPS. It shows you what runtime you can expect at a few different load amounts.

http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=17

KVAr_apc
Captain
Captain
0 Likes
0
116

Re: Check of the UPS runtime

This was originally posted on APC forums on 9/21/2007


Power factor doesn't matter for the most part for runtime test. You just want the load to simulate what your expected backup load is using in watts.

If you're doing a general UPS calibration, charge 24 hours, then use resistive load (like light bulbs) with 30-50% the wattage rating of UPS and let it run until it shuts off on its own.