Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Changing battery on a Back-UPS ES 725

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Changing battery on a Back-UPS ES 725
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
11
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

Changing battery on a Back-UPS ES 725

I attempted to change the battery in my ES 725 yesterday, and when I restarted the computer, it tells me the battery is diconnected, double and triple checked, and it was connected, I don't see any way it could be connected differently. Does that mean my unit is bad? Seems unlikely, since it was working fine until I changed the battery, even with reinstalling the old battery, it does the same thing. Any ideas?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

How exactly did you connect the battery to your computer?



























-________________________
George Alarcon
[find cheap flights cheap airline tickets|http://www.cheapairfare.vg]
[how to lose weight fast|http://www.weight-loss.vg]
[mercury poisoning treatment mercury detox|http://www.mercurypoisoning.me ]

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

Thanks, I am probably just going to keep this LS-700 that my friend gave me, he said it was an extra he had anyway, it's working fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

Hello,

When you doublechecked the battery connections, were both the red and black wires still securely connected, or had one/both of them come loose at all?

What was the exact message that you were receiving and where were you receiving it from? Are you using Powerchute of some kind? If so, which version (you can find this under Help/About in the Powerchute interface)?

Was the Back UPS making any sort of tones or beeping sounds when you experienced the problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:21 PM . Last Modified: ‎2024-03-21 03:46 AM

I did not check thw wires, just the connectors, I don't have the ups connected at this time, so I can't get the details of the message. Yes, I am using Powerchute. version Personal Edition 1.5. Yes, I was getting a constant tone from the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

Hello,

Okay, if you were getting a constant tone then that would possibly indicate a disconnected battery.

I would just doublecheck the connection of the red and black wires again. When you slide the bottom cover off, make sure that red is connected to red and black is connected to black, and that they still have a secure connection. If they are connected securely, then the problem could be a faulty wire or perhaps a bad battery. Where did you get the new battery from and how long had the original battery been reported as bad?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

Hello,

Did you have a chance to check the battery connections?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

Just did it today, somehow when disconnecting the battery wire, the on-off switch broke, so that's what the problem was, I'm using a unit belonging to a friend right now, don't know if it would be cost effective to repair the725.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

What is the serial number off of the UPS? You may want to just consider trading the UPS in for a discount on a brand new unit. This is called our Trade-UPS program and can be found through the following link:

http://www.apc.com/buy/index.cfm

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

I attempted to change the battery in my ES 725 yesterday, and when I restarted the computer, it tells me the battery is diconnected, double and triple checked, and it was connected, I don't see any way it could be connected differently. Does that mean my unit is bad? Seems unlikely, since it was working fine until I changed the battery, even with reinstalling the old battery, it does the same thing. Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

I also have the UPS ES 725. After 4 years I replace the battery and it quit working. It gives the continuous tone sound. I called Tech. Supt. already and they said let the unit charge for 8 hours before you turn it on. I have no idea what?s that?s about.
Apparently these old 725 units have faulty wiring and the first time you change the battery the wires breaks or gets loose somewhere. I can't believe I spent with shipping about $50.00. For that price I could all most bought a new unit.
What is this upgrade all about? Since I now have a battery can I get a unit without a battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

Hello,

We do not sell units without the battery, but you could partake in our Trade UPS program and either just hold on to the battery for future use, or ship it back with the pre-paid shipping label that is included.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

0 Likes
0
2277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 PM . Last Modified: ‎2024-03-21 03:46 AM

How exactly did you connect the battery to your computer?



























-________________________
George Alarcon
[find cheap flights cheap airline tickets|http://www.cheapairfare.vg]
[how to lose weight fast|http://www.weight-loss.vg]
[mercury poisoning treatment mercury detox|http://www.mercurypoisoning.me ]

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore