I'm replacing a Smart-UPS 10000DP with a Smart-UPS 10000XLI, can I wire it to the SUDP002 service/maintenance Panel that the old one was wired to?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 PM . Last Modified: 2024-03-21 01:35 AM
Hi Peter,
I'm assuming the 10000XLI you mean is the Smart-UPS RT. If so and as long as you are using the RT in single phase mode then the SUDP0002 should work fine.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 PM . Last Modified: 2024-03-21 01:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 PM . Last Modified: 2024-03-21 01:36 AM
Thanks Powerman, it is a Smart UPS RT in single phase mode, I shall go ahead
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 PM . Last Modified: 2024-03-21 01:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 PM . Last Modified: 2024-03-21 01:36 AM
Powerman your are wrong!!
Hi Jakub,
Can you still turn the bypass switch manually
Pete
Response (Jakub Wolski) - 04/07/2009 10:27 AM
Dear Peter,
No, if there is no communication you are not able to turn any switches at the bypass panel manually. If you check the operation manual http://www.apcmedia.com/salestools/ASTE-6Z8LBS_R0_EN.pdf
page number 13 "How to Switch From Normal to Bypass Mode"
1. Press and hold the S002 switch and, within one (1) second turn the Q002 switch to the Bypass position.
2. Turn the Q001 switch to the “0” position. The UPS can now be shut down or serviced.
When you are pressing the "S002 switch" SUDP002 is checking with the UPS if UPS is in normal operation and if is safe to switch to bypass operation. If it is, the H002 LED will lit ON and you are able to switch the Q002 ON.
"Before operating the SBP, check that the Smart-UPS DP is running in normal operation. When S002 is pushed, H002 must go on within 1 second - if not, release S002 immediately- bypass mains is outside tolerances and the SBP cannot be operated."
If there is no communication bypass will never get this information and you will be not able to put UPS in bypass.
Regards
Jakub Wolski | Technical Support Engineer - UK and Ireland
APC-MGE Customer Care Center United Kingdom
Message was edited by: PeterC
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 PM . Last Modified: 2024-03-21 01:35 AM
Hi Peter,
I'm assuming the 10000XLI you mean is the Smart-UPS RT. If so and as long as you are using the RT in single phase mode then the SUDP0002 should work fine.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.