I just installed my new UPS and the next night we had a storm where the power flickered off and on at some point. The UPS constant alarm started and the screen showed the F02 fault. I've read that this is a fairly common fault and I'm quite discouraged that a brand new UPS can't handle a short power outage.
After shutting it off and restarting it seems fine. The log from the ups daemon seem to indicate that at 23:17 it handled a very short failure but then sometime around midnight the daemon was restarted after I turned the UPS back on. So there is no log information about the fault:
2025-04-03 00:17:11 -0400 apcupsd 3.14.14 (31 May 2016) debian startup succeeded
2025-04-02 23:17:23 -0400 Power is back. UPS running on mains.
2025-04-02 23:17:21 -0400 Power failure.
2025-04-02 14:05:50 -0400 apcupsd 3.14.14 (31 May 2016) debian startup succeeded
Today I unplugged the power to the unit to make sure it was working and it switched to battery operation without problem. I also tried running the "apctest" program in order to run a self test but it doesn't seem to work. Does this model have a self test feature?
Select function number: 2
This test instructs the UPS to perform a self-test
operation and reports the result when the test completes.
Clearing previous self test result...CLEARED
Initiating self test...INITIATED
Waiting for test to complete...TEST DID NOT COMPLETE
Is this a faulty unit? The battery in this "brand new" unit was installed a year ago. I hope this doesn't mean I've already lost a year of lifetime.
Any help / suggestions appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-04-19 05:16 AM
A F02 error code is (On Battery) output short. Meaning the system has detected a connected device is shorted causing the failure.
Turn the system off and disconnect all connected loads. Turn the system back on and add one load at a time.
If the F02 error code returns that specific load is potentially faulty.
Questions Ask . . .
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-06-22 11:16 AM
UPDATE: I received a replacement product from SE about a month ago. It was identical to the original - similar old battery date and same firmware. Yesterday during a power outage the replacement also failed and shutdown. This product is not functioning as a UPS - I would not recommend purchasing it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-06-23 03:15 AM
I would suggest you contact APC Technical Support to have this resolved. In the interim provide the following logs from PCSS: Event, Data, UPS.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of