Batteryvoltage raises continously if Battery is not installed

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Batteryvoltage raises continously if Battery is not installed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:14 AM . Last Modified: ‎2024-03-26 10:39 PM

0 Likes
1
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:14 AM . Last Modified: ‎2024-03-26 10:39 PM

Batteryvoltage raises continously if Battery is not installed

I ordered a new Replacement Battery for one of my Back-UPS RS800 (RBC32) which did not work in any of my 3 UPS.
The Phenomen was that the Battery had 12.1V directly after removing from the UPS and raised continously up to over 18V!
All UPS gave me the Error "Overload" and "Replace Battery". After my 3rd Call to APC, they promised me to send me a new
Battery and that I can throw the bad one, even if it is a new one....

Thank You APC for the good Support

I have to put the bad Battery outside because I don't know what happens when the Voltage raises any more....

Update: this morning, the Battery had 18.85V and is raising further

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:14 AM . Last Modified: ‎2024-03-26 10:39 PM

0 Likes
0
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:14 AM . Last Modified: ‎2024-03-26 10:39 PM

Hi Christian,

The RBC32 is actually a 24vdc battery configuration. The nominal voltage of the battery should read around 24-25vdc, when disconnected from the UPS following an adequate charge. The fact that you were reading 12.1vdc following immediate removal from the UPS would lead me to believe the battery is old and is under significant strain when installed. Once removed from the configuration, the battery will naturally attempt to return to the nominal state or battery voltage in this case.

Secret Squirrel

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:14 AM . Last Modified: ‎2024-03-26 10:39 PM

0 Likes
0
452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:14 AM . Last Modified: ‎2024-03-26 10:39 PM

Hi Christian,

The RBC32 is actually a 24vdc battery configuration. The nominal voltage of the battery should read around 24-25vdc, when disconnected from the UPS following an adequate charge. The fact that you were reading 12.1vdc following immediate removal from the UPS would lead me to believe the battery is old and is under significant strain when installed. Once removed from the configuration, the battery will naturally attempt to return to the nominal state or battery voltage in this case.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore