Battery connector correctly connected?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Battery connector correctly connected?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Back-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
TomPouceOnline
Ensign TomPouceOnline
Ensign

Posted: ‎2022-10-28 06:49 AM

2 Likes
14
25270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-28 06:49 AM

Battery connector correctly connected?

Hi

 

I got a new BX750MI Back-UPS.

 

1) According to the attached picture, is the yellow battery connector enough pushed? I can start the UPS but I would like to avoid any battery disconnection because of bad contact.

 

2) If I need to disconnect the battery, do I just need to pull the connector strongly?

 

Thanks in davance for your feedback.

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • battery connector
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-17 06:58 PM

In response to TomPouceOnline
0 Likes
1
24943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-17 06:58 PM

Hi @TomPouceOnline 

 

Apologies for the delay in my response, I have checked with our UPS Experts and was advised that if it doesn't get fully inserted we just need to make sure that it makes contact to close the circuit.

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-03 10:43 PM

0 Likes
1
25182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-03 10:43 PM

Hi @TomPouceOnline 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.

 

I strongly suggest that you try to push it in more.  The metal shouldn't be exposed and the yellow plastic should seal it.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TomPouceOnline
Ensign TomPouceOnline
Ensign

Posted: ‎2022-11-06 04:17 AM

In response to JonPro
1 Like
0
25158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-06 04:17 AM

Hi @JonPro 

 

Thanks a lot for your feedback. I tried to push more but it seems it is not possible. Do you have a picture of this battery connector type correctly sealed in?

 

Regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Abdullah07
Crewman Abdullah07
Crewman

Posted: ‎2022-11-06 06:31 AM

0 Likes
0
25154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-06 06:31 AM

Hi @TomPouceOnline 

My Name is Abdullah. If You want to pull out you need to tester or straight screw 🪛 and full with it.

Thanks 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Abdullah07
Crewman Abdullah07
Crewman

Posted: ‎2022-11-06 06:37 AM

0 Likes
7
25153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-06 06:37 AM

@TomPouceOnline 

Hi I see in picture your battery connector perfectly fitted. I think Your battery is dead need to replace

Tell me about duration of Purchase or UPS usage for more details 

  • Tags:
  • battery
  • english
  • replacement
Reply

Link copied. Please paste this link to share this article on your social media post.

TomPouceOnline
Ensign TomPouceOnline
Ensign

Posted: ‎2022-11-07 12:58 AM

In response to Abdullah07
1 Like
6
25129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 12:58 AM

Hi @Abdullah07 

Why do you say the battery is dead? The UPS is new. My only concern is about the battery connector type which is different from my former BX700UI. With the old model the connector was completely pushed into the UPS body. This doesn't look the same with the new connector type on the BX750MI (do you confirm @JonPro ?).

 

Regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-07 04:11 AM

In response to TomPouceOnline
0 Likes
5
25116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 04:11 AM

@TomPouceOnline 

 

I found a video on how UPSs that use this kind of battery connector is being used.  You can skip to the 0.10 seconds mark of the video.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TomPouceOnline
Ensign TomPouceOnline
Ensign

Posted: ‎2022-11-07 10:55 AM

In response to JonPro
0 Likes
4
25097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 10:55 AM

Hi @JonPro 

 

Thanks for the video. However this is the old connector type (like for the BX700UI). For the BX750MI the connector is different.

 

Regards

Thomas

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-07 05:39 PM

In response to TomPouceOnline
0 Likes
0
25088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 05:39 PM

Let me check on this further.  By any chance, have you raised a case with our Technical Support team?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Abdullah07
Crewman Abdullah07
Crewman

Posted: ‎2022-11-07 06:00 PM

In response to TomPouceOnline
0 Likes
0
25085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 06:00 PM

Yeah in picture battery connector connected correctly. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-17 06:58 PM

In response to TomPouceOnline
0 Likes
1
24944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-17 06:58 PM

Hi @TomPouceOnline 

 

Apologies for the delay in my response, I have checked with our UPS Experts and was advised that if it doesn't get fully inserted we just need to make sure that it makes contact to close the circuit.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TomPouceOnline
Ensign TomPouceOnline
Ensign

Posted: ‎2022-11-18 09:56 AM

In response to JonPro
1 Like
0
24936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 09:56 AM

Hi @JonPro 

 

Thanks a lot for your valuable feedback.

 

With best regards

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

fosiqqqq
fosiqqqq
Cadet

Posted: ‎2024-05-14 03:34 AM

0 Likes
1
16235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-14 03:34 AM

So I have the same problem and I still don't know if I should try to push it more or it should stay like in the picture from first post?

Reply

Link copied. Please paste this link to share this article on your social media post.

koby100
koby100
Cadet

Posted: ‎2024-05-15 07:51 AM

In response to fosiqqqq
0 Likes
0
16174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-15 07:51 AM

I had the same Issue. The yellow battery connector does not get fully into the UPS.
I searched many posts about this issue and found out that it is OK.

Strange design, but the UPS works great.

Reply

Link copied. Please paste this link to share this article on your social media post.

mosp
mosp
Cadet

Posted: ‎2024-05-28 08:14 AM

0 Likes
0
15778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-28 08:14 AM

Just got a new BX750MI-FR and I could not get push the connector all the way in. After 24hours of charging I connected a printer and the UPS started beeping. Removed the printer and tried to push in the connector further, this time I succeeded, but after connecting a rinter the beeping sounds came back. I have no windows laptop to install Powerchute. Is there another way to check the battery?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore