Battery backup problem

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Battery backup problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
5
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

Battery backup problem

I have an APC BACK-UPS ES 400. All of a sudden, the battery backup doesn't work. If there is a power failure or I unplug the power cable, the battery doesn't work. The light is green so it doesn't appeal to be a battery problem.

I've tried to push the circuit breaker button, but I'm not a le to press it. I don't know if it is me or if it is the button that is broken.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

Can you confirm the exact SKU of the UPS from the white sticker on the back or bottom? I think this unit is an older design so I am not sure how many LEDs it has. I want to find a picture once I know the model SKU from the sticker. When you unplug the power cable, does the UPS turn off too? How old is the battery?

The circuit button button is always sticking out about at least 1/4 inches or 1cm or so. If it was actually tripped, it'd be out at least one inch to 1 1/4 inches or a few centimeters.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

The sticker says: BE400-GR     7B1121L03411

When I unplug the power cable, the USP doesn't turn off, it is on and the light is green.
The circuit breaker doesn't stick out from the UPS. I can't press it because it appears to be already pushed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

All outlets work when UPS is on and plugged in. The problem happens when there is a power outage or I unplug the UPS manually, in that case, none of the outlet work and it beeps only a few times and not 4 times every 30 seconds as usual. Neither the surge only nor the battery backup+surge protection work when there is no power cable connected of during a power outage.

I checked the manual page 2 under "Connected equipment loses power". No one of those cases apply to me. I'm sure there is no overload because I have the same electronic devices connected to the UPS for a few years and the problem is recent.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

Can you confirm the exact SKU of the UPS from the white sticker on the back or bottom? I think this unit is an older design so I am not sure how many LEDs it has. I want to find a picture once I know the model SKU from the sticker. When you unplug the power cable, does the UPS turn off too? How old is the battery?

The circuit button button is always sticking out about at least 1/4 inches or 1cm or so. If it was actually tripped, it'd be out at least one inch to 1 1/4 inches or a few centimeters.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

The sticker says: BE400-GR     7B1121L03411

When I unplug the power cable, the USP doesn't turn off, it is on and the light is green.
The circuit breaker doesn't stick out from the UPS. I can't press it because it appears to be already pushed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

Thank you. So the UPS is not that old in reality.

All outlets work when the UPS is turned on and plugged in, there is a power outage or you unplug the UPS manually and the Battery Back Up + Surge Outlets turn off but the UPS remains on (and beeps 4 times every 30 seconds)? Do the Surge Only outlets remain on during this time (if you're using them or could test)?

According to the user's guide @ http://www.apcmedia.com/salestools/ASTE-6Z7V9N/ASTE-6Z7V9N_R1_EN.pdf there are a few possibilities. You'd want to make sure you see the same behavior with a small load versus possibly overloading it to rule that out (though with an overload, you'd hear a loud solid tone). I don't think it's that so I'd try to confirm you ruled out everything else for "Connected equipment loses power." on page 2.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

All outlets work when UPS is on and plugged in. The problem happens when there is a power outage or I unplug the UPS manually, in that case, none of the outlet work and it beeps only a few times and not 4 times every 30 seconds as usual. Neither the surge only nor the battery backup+surge protection work when there is no power cable connected of during a power outage.

I checked the manual page 2 under "Connected equipment loses power". No one of those cases apply to me. I'm sure there is no overload because I have the same electronic devices connected to the UPS for a few years and the problem is recent.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:30 AM . Last Modified: ‎2024-03-27 03:32 AM

If you are having a problem with the surge only outlets as well, it sounds like an internal problem with the UPS unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore