Battery Backup BX1500LCD Problem
I get this message. The battery in your battery backup is disconnected. The unit will not be able to support your system in the event of a power problem until you connect your battery. I checked the battery voltage and is as follows. 12.17, 13.40. The other message that pops up is. Battery reconnected in battery backup. Can you advise.
- Labels:
-
Back-UPS & Surge Protectors
- Tags:
- Harley51
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:39 AM . Last Modified: 2024-03-27 02:14 AM
Dale,
The voltage for the battery pack should be between 26 and 27 volts. If your battery pack is only reading 12.17, 13.40 the battery pack needs to be replaced. If you pulled the battery pack apart and are measuring the individual batteries 12.17 is also low and the pack should be replaced.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:39 AM . Last Modified: 2024-03-27 02:14 AM
Dale,
The voltage for the battery pack should be between 26 and 27 volts. If your battery pack is only reading 12.17, 13.40 the battery pack needs to be replaced. If you pulled the battery pack apart and are measuring the individual batteries 12.17 is also low and the pack should be replaced.