Backup ups xs 1300 question

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Backup ups xs 1300 question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
109
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:50 PM

0 Likes
11
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:50 PM

Backup ups xs 1300 question

We're using backup UPS XS 1300 in our office as a power backup for the office computer & the security board. This one:

https://www.amazon.com/APC-1300VA-Battery-Discontinued-Manufacturer/dp/B000XFXEDW

We had it for quite a while. So last saturday I noticed that the equipment was completely dead. I checked and the issue was this UPS. I tried to restart it by holding the power button, but it refused to start. I was giving off fast beeps when I was holding down the power button. I was able to eventually get the power back on by unplugging this UPS and plugging everything directly into the wall.

Also note that the power did not go out that night. (I can tell by the Microwave clock still being on.) So for some reason this UPS did what it was supposed to guard against -- it killed the power when the wall power was still on 🙂 Also note that I had both computer and the security board plugged into the battery section of the UPS.

So I'm curious if this issue is with the battery or with the unit itself? I don't want to pay for a new battery only to discover that I need to buy a new UPS itself.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Usually, that is how they work.  They will still flicker on power if the power is cut since there isn't a battery, but usually they will still operate with a bad battery.  I think some models vary in this now, but this is how all of our older models operate.

As far as making them so the battery isn't 'inline' but more standby--maybe that's how they used to make them and that's why our older ones don't just flat out die with a bad battery.  And the only reason I could think of that you'd move them back to being inline--cost.  Which would make sense on some of the lower end or midscale models like the back ups series.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:50 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:50 PM

I had the exact same thing happen a few years back with one of our point of sale UPSs.  We replaced the battery and all has been well since then.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Thanks for the reply. Just curious though, did your unit also cut off power when the battery went dead? This is exactly why we're buying these things so that IT DOES NOT happen!

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Yep, sure did.  Closed the business one night and went back in the next morning and it was dead and pos system was off (which cost us some lost revenue).  Luckily it was an easy enough fix to just plug everything directly (or I think I used a spare UPS--can't remember), and once we had a replacement battery all was good.  I was concerned that the UPS might had gone bad and posted here to ask, but it was just the battery.

Here's a link to that original post years ago:

http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/11535/sc620-just-died-all-of-...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Oh, wow. Thanks for sharing.

So what do you do now? Do you use the same unit? I'm thinking to get a different brand. I mean, it's ridiculous that it just cuts out the power when the battery dies even though the wall power is still on. Ours gave no audible indication of the problem earlier.

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

I use the same brand and the same unit.  APC units usually give warning well in advance of their batteries dying.  This is the first out of dozens of units we have that didn't, so I think it was the exception to the rule vs the usual case.  The usual case will either seeing the replace battery light at some point because of a failure on a self-test or after a power outage when the load was dropped.  It can be intermittent indicating the battery has a bit of life left, but generally once the replace battery light is on, it's time to replace it.

We still buy APC units almost exclusively because of their longevity.  We have units that are 20 years old that just need an APC battery every few years.  I don't think the other brands products would last like this as they have not been exclusively making ups's as long as APC.  

Now if I find a deal on another brand (like a recent find on triplite units in the cdw outlet) when I'm looking for a replacement battery, I will try another brand's unit.  But I don't have as much faith in them simply because I've seen APC units last so long.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Hey, Thanks. Good to know. You're very helpful!

Just from curiosity. How do you pick a UPS unit? Is it the wattage of the stuff that's being plugged into it or what?

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Usually based on the price and the warranty, lol.

Except when I'm actually sizing it for a particular load.  Then to have any decent runtime, I take the number of watts (at 120v) and multiply it by 2 to get the bare minimum VA for the load.  (Keep in mind this isn't the calculation for VA, but it's a rough estimate.)  If I can get more VA, even better as that will extend the runtime.

What I have recently found out is that while the VA sizing for upses generally doesn't change based on the operational voltage (120v/220v/240v), the runtime changes dramatically, decreasing for the same wattage device on higher voltage systems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

I'll be honest. This thing gave me a lot of headache. Main point is that it shouldn't be shutting off by itself when the battery dies without any warning. Why do we even need it then 🙂
So I decided to change companies. Picked this " CyberPower AVRG750U AVR UPS System, 750VA/450W, 12 Outlets ":
https://www.amazon.com/CyberPower-AVRG750U-System-Outlets-Compact/dp/B00K8ZMTAQ/ref=cm_cr_arp_d_prod...
Will see how it performs. If it does as badly as this one then I'll probably be better off with just a surge protector.
Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Keep in mind that once the battery is past the changing point, any UPS will do this immediate dying thing.  And for the record I've seen more of other brands do this than APC.  I have a cyberpower one right now that was pulled out of service years ago for doing that.  Still haven't had time to replace the battery...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Sure. There's no other way to see other than just to get one and try it.

PS. On the side note, how come they can't make them so that the unit starts drawing power from the wall when the battery dies instead of just throwing the towel?

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

0 Likes
0
2084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-26 10:49 PM

Usually, that is how they work.  They will still flicker on power if the power is cut since there isn't a battery, but usually they will still operate with a bad battery.  I think some models vary in this now, but this is how all of our older models operate.

As far as making them so the battery isn't 'inline' but more standby--maybe that's how they used to make them and that's why our older ones don't just flat out die with a bad battery.  And the only reason I could think of that you'd move them back to being inline--cost.  Which would make sense on some of the lower end or midscale models like the back ups series.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore