Backup UPS 1300 self test drains battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Backup UPS 1300 self test drains battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-29 10:14 PM . Last Modified: ‎2024-03-19 11:40 PM

0 Likes
1
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:14 PM . Last Modified: ‎2024-03-19 11:40 PM

Backup UPS 1300 self test drains battery

Battery in Backup UPS 1300 goes from 100% to about half that after self test, even though readout says the device passed the self test. It takes several hours for battery to get back to 100%. I first realized that there was a problem with the unit when alarm went off, with message that the device was overloaded. Only have tiny load on device, so not sure what triggered the alarm other than, perhaps, an automatic self test. Battery is several years old and due for replacement. My concern is that there may be another problem with the unit and that a new battery is not the proper fix. In short: is the drop-off in charge after a self test a normal occurrence for a aged/weak battery or could there be another problem with the UPS? Thanks.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:14 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:14 PM . Last Modified: ‎2024-03-19 11:39 PM

Everything sounds strictly like "old battery" beyond the mysterious overload message. When the battery percentage drops a lot during the self test, yes this is typically a sign of the battery aging and losing its overall capacity.

Did you see the UPS is overload message on the front LCD screen or where specifically? Did the UPS turn it's output off after this or did it pop and go away quickly and that's it?

And by "several" years old - how many years? 3-5?

I can't be 100% sure as with many of the issues and specific symptoms but there is nothing you've said so far that would not make me think a battery is the right option at this time. If you're worried though, you always have the UPS Trade UPS option to trade the UPS in, even with a bad battery, and get a discount on a new one with a new warranty on both the UPS and battery. Let me know if you want further details.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:14 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
1233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:14 PM . Last Modified: ‎2024-03-19 11:39 PM

Everything sounds strictly like "old battery" beyond the mysterious overload message. When the battery percentage drops a lot during the self test, yes this is typically a sign of the battery aging and losing its overall capacity.

Did you see the UPS is overload message on the front LCD screen or where specifically? Did the UPS turn it's output off after this or did it pop and go away quickly and that's it?

And by "several" years old - how many years? 3-5?

I can't be 100% sure as with many of the issues and specific symptoms but there is nothing you've said so far that would not make me think a battery is the right option at this time. If you're worried though, you always have the UPS Trade UPS option to trade the UPS in, even with a bad battery, and get a discount on a new one with a new warranty on both the UPS and battery. Let me know if you want further details.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore