Back-UPS 1100 U-LM - Equipment Dropping

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS 1100 U-LM - Equipment Dropping
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-26 11:06 AM . Last Modified: ‎2021-07-26 08:58 PM

0 Likes
5
1811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-26 11:06 AM . Last Modified: ‎2021-07-26 08:58 PM

Back-UPS 1100 U-LM - Equipment Dropping

Hey folks,

 

You probably see this alot. I have both my PC and modem power cords connected to my Back-UPS Surge protector+Backup Battery outlets, but whenever I have a power cut my modem drops.

 

I unplugged my Back-UPS from the wall socket so everything is using power directly from the Backup-UPS, but when I have a power cut, it's still dropping, which is very strange.

 

I should say that I had to run an extension cord from my Modem > Extension > Back-UPS, but my PC is connected in a similar way as well but it doesn't have the same issue.

 

That said, my modem is quite a distance away so I'm wondering if that distance is a factor. I have my sensitivity set to high. 

 

Thanks so much.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 06:30 AM

In response to Anonymous user
0 Likes
0
1763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 06:30 AM

Hi @Anonymous user,

 

If the modem will run when the UPS is warm started/running off of battery but drops when there is a cut over from street power to the battery, the issue may be the transfer time. When a Back-UPS switches from street power to the battery, there is a transfer time. Depending on the model and the sensitivity, there can be a 6 to 8 (high sensitivity), 8 – 10 (Medium sensitivity), and 12 - 14 millisecond transfer delay.

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-27 05:23 AM

0 Likes
4
1785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-27 05:23 AM

Hi,

 

The voltage may be dropping due to using the extension cord and the UPS switching to the battery. It may be the modem does not like the sinewave output of the Back-UPS or a combination of the two. For more information on the sinewave, see https://www.upsbatterycenter.com/blog/what-is-a-square-wave/

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-27 05:57 AM

In response to BillP
0 Likes
3
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-27 05:57 AM

Thanks for your reply. I'm curious as to why the modem would still drop even when the Back-UPS is completely unplugged from the wall and using the battery.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 06:30 AM

In response to Anonymous user
0 Likes
0
1764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 06:30 AM

Hi @Anonymous user,

 

If the modem will run when the UPS is warm started/running off of battery but drops when there is a cut over from street power to the battery, the issue may be the transfer time. When a Back-UPS switches from street power to the battery, there is a transfer time. Depending on the model and the sensitivity, there can be a 6 to 8 (high sensitivity), 8 – 10 (Medium sensitivity), and 12 - 14 millisecond transfer delay.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-07-29 11:56 AM . Last Modified: ‎2021-07-29 12:02 PM

In response to Anonymous user
0 Likes
1
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 11:56 AM . Last Modified: ‎2021-07-29 12:02 PM

There are some ways to solve this at all but unfortunately none of them are cheap.  Here are my two cents idea 

 

Option 1:  Replace your UPS with a double conversion one, it always will output pure sinusoidal AC and there is not transfer time.

 

Option 2:  if your modem is powered with  12 volt  DC and you are handy with electronics you could use a 12 volt 18 Amp SLA battery, a smart car battery charger  like the NOCO Genius 10 , a couple of 5 amp  diodes, a automotive 5 amp fuse and it's matching fuse  holder  as  to make a dual  12 volt power supply to keep your modem always powered.    The setup is quite simple:     cut the positive wire of the cable that feed the modem and  connect the side that goes to the modem to both diodes negative side  joined  ( solder them together and protect the joint  with tape or heat shrink tube) . Then solder the positive side of one of the diodes to the positive wire that you cut before which   goes to the modem original transformer ( protect the joint  with tape or shrink tube) .  Hook with   screws and nuts  the NOCO battery charger plugin adapter positive and negative ( it's included in the charger box with the clamp adapter)  to the SLA  Battery. Hook the battery positive through the fuse holder  to the remaining positive diode side. Hook the SLA battery negative to the negative wire of the cable that goes from the original modem power supply to the modem. ( Splice or solder the joint and protect it with tape or heath shrink tube). Double check the installation. Plug the NOCO charger to the connector adapter, then to AC and set it to AGM battery type. Seconds later It should start to charge the battery.  Plug the modem OEM power supply and check if the modem works fine. Unplug it and now insert the 5 amp fuse in the fuse holder and check the router operation. If it's powering fine then you are ready to plug the OEM power supply to the wall and the NOCO AC plug to the UPS  ( it work fine with any UPS). 

With this setup your modem will be always  powered with pure DC and provide you with many hours of un interrupted internet in case there is a long power outrage. 

 

  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-29 12:07 PM

In response to robmir_apc
0 Likes
0
1745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 12:07 PM

Thanks a lot. I appreciate the help!
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore