Back-ups BX1500G fails automatic self test

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-ups BX1500G fails automatic self test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
8
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

Back-ups BX1500G fails automatic self test

I got this ups a month or so ago. Twice (in the middle of the night) it has initiated a self test that fails and reports a bad battery. Causing my server, NAS box, and other equipment to go down. Load status is around 10%.

If I shut it down and turn it on, the power on battery test passes.

The software reports that a manual test failed (I never ran one). There is no other information as it is all lost when the UPS fails.

The software identifies the UPS as an XS 1500G.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

about a week ago I was off of work and had a chance to call support. Although the lady I talked to seemed highly confused about everything APC did send me out a replacement unit. I hooked it up to the same equipment, it started up, and passed the POST. I waited for it to fully charge and did a manual self test and it passed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

Hi Robert,

The UPS will perform an automatic Online Selftest when the unit is first powered on. It will then perform an automatic self test every 14 days following. With no load powered on during the initial turn on, the UPS will invariably pass unless a truly damaged battery is detected. In your case, we may be dealing with a battery which is too weak to support your configuration during these automatic self tests.

You've indicated the unit was acquired 1-2 months ago, however it's not clear how old the unit actually is. Depending upon where the unit is purchased, it may have been in new stock for a period of time. The internal battery will generally be shipped from manufacturing at approx. 80% charge capacity and can stored without charge for up to one year without the need for recharge. 

If you could respond with the unit's serial number and a comprehensive list of product plugged into the unit's battery outlets, we may have a better understanding of why the units is responding as it is.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

yesterday morning at 4:30am it did the self test and failed (which woke me up). I then went to it, powered it off and back on (less than 5 minutes), and it passed the power on self test. I bought it February 20th of this year, and the date the software says the battery was installed is 9-6-2016 there was a printout on the unit that said the same thing I do not have it anymore.. serial number is 3B1636X08220. The unit has connected to it:

Dell Vostro 200 with LCD monitor

Qnap ts-231

Sonicwall TZ-200

the software shows only about 10 to maybe 13% load.it reports the unit is an XS 1500g.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

Hi Robert,

Considering the young age of the unit and small load, it would lead me to believe the issue is battery related. I would recommend you contact Schneider Electric technical support for an in warranty replacement of your battery. 

Call: 800-800-4272 Option $ for Technical Support / Option 2 For Back-UPS / Surge Support

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

Robert,

Your PC Dell Vostro 200 has a PFC power supply. They don't always work with a Modified sinewave UPS.

Do you have the sensitivity set to High in the UPS software?

  • Tags:
  • pfc
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

Let me see if I understand this?

My computer has a PFC power supply (had to look that up) that doesn't like the output of ups's, and this is causing my UPS to report the battery is bad?

I am not sure of the correlation here.

The previous UPS was a very old 1250 back-ups UPS that worked fine with this UPS but i replaced it because the batteries were a pain to replace. it also had a modified sine wave.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

I just pulled the batteries out and put them in another 24v ups, then did a self test and they passed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

On 26/3/2017 2:22 AM, Robert said:

I just pulled the batteries out and put them in another 24v ups, then did a self test and they passed.

Did you have a good load on the UPS at the time? Self test relies on switching to battery and observing their behaviour. If theres little or no load an almost dead battery can quiet comfortably pass a self test.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-27 12:42 AM

about a week ago I was off of work and had a chance to call support. Although the lady I talked to seemed highly confused about everything APC did send me out a replacement unit. I hooked it up to the same equipment, it started up, and passed the POST. I waited for it to fully charge and did a manual self test and it passed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore