Back-Ups RS 1100 shuts off when line voltage becomes low. Why?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-Ups RS 1100 shuts off when line voltage becomes low. Why?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:53 PM . Last Modified: ‎2024-03-21 01:28 AM

0 Likes
7
3593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:53 PM . Last Modified: ‎2024-03-21 01:28 AM

Back-Ups RS 1100 shuts off when line voltage becomes low. Why?

I have an APC Back-Ups RS 1100 for the past 2 years and it started to show a weird problem from the past week. The UPS is working perfectly fine with good backup time, no battery warnings etc. But the UPS just shuts  itself off when the line voltage drops below 180v and emits a constant beep until I turn it off. I have tried all sensitivity modes but of no use. The UPS is supposed to go on battery when the line voltage drops but here it just turns off with a constant beep. But when there is a complete power outage the UPS works fine, transfers to battery and gives good backup time and returns to line when the power is restored. But if the power is restored by anything less than 180 volts, then it shuts off and starts to beep continuously until I turn it off. Backup is fine and it is handling the load well. And this model don't have any software support and I can't doubt the batteries since they are just 2 years old. What could be the problem here?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:28 AM

0 Likes
0
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:28 AM

I too have a realistic issue at hand:

The APC Back-UPS RS 1100 is supposed to protect computers, monitors and other equipment, as it also includes a surge protector. But one place where it fails is, if it switches back from an incoming Inverter supply to the Normal Power supply. The UPS totally trips and the Computer restarts. Somehow the Computer has been able to withstand so many re-starts, but some data loss has occurred on the Computer. Having used other UPSes before like Microtek, CompactUPS and a few others that never Trip totally when switching back from an Inverter power supply to the Normal Power supply, I am shocked and dismayed at such occurrence on a UPS being offered by such an advanced company that specializes in UPSes. It seems that a company of the size and know how as the American Power Conversion has not been able to customize their UPS's to the Indian environment, where most of the homes are equipped with an inverter because of the unsure power supply in most of the parts of the country. An inverter would be connected to the whole supply to the home. In view of this, making sure that the UPS does not get the Inverter power input is pretty difficult to setup. After going through the Manual, where a change is recommended in the sensitivity of the UPS and making the change, it did not improve the fact that the UPS trips totally when switching from an Inverter supply to the Normal Power supply. Sometimes, it makes one wish not to go for costly known products that do not perform, and rather stick to local/unknown brands that are more reliable.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:53 PM . Last Modified: ‎2024-03-21 01:28 AM

0 Likes
0
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:53 PM . Last Modified: ‎2024-03-21 01:28 AM

Can you provide the part# of your BackUPS?

1007_Findyourmodel%23.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:53 PM . Last Modified: ‎2024-03-21 01:28 AM

0 Likes
0
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:53 PM . Last Modified: ‎2024-03-21 01:28 AM

MODEL NO: BR1100CI-IN

Serial No: EB1037001480

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:28 AM

0 Likes
0
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:28 AM

Your UPS may already have an internal fault. Can you try to brain dead or de-energize the UPS?

To brain dead a Back-ups is to purge the charge in the brain of the UPS. To do this, follow the below procedure:

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the ""On"" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

If doing the above steps do not resolve the issue, I suggest that you get in touch with your local technical support to verify the warranty and have the unit replaced if necessary. Hit the link then choose the India from the country selection drop down. I hope this helps

Contact Us



Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:28 AM

0 Likes
0
3593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:28 AM

I too have a realistic issue at hand:

The APC Back-UPS RS 1100 is supposed to protect computers, monitors and other equipment, as it also includes a surge protector. But one place where it fails is, if it switches back from an incoming Inverter supply to the Normal Power supply. The UPS totally trips and the Computer restarts. Somehow the Computer has been able to withstand so many re-starts, but some data loss has occurred on the Computer. Having used other UPSes before like Microtek, CompactUPS and a few others that never Trip totally when switching back from an Inverter power supply to the Normal Power supply, I am shocked and dismayed at such occurrence on a UPS being offered by such an advanced company that specializes in UPSes. It seems that a company of the size and know how as the American Power Conversion has not been able to customize their UPS's to the Indian environment, where most of the homes are equipped with an inverter because of the unsure power supply in most of the parts of the country. An inverter would be connected to the whole supply to the home. In view of this, making sure that the UPS does not get the Inverter power input is pretty difficult to setup. After going through the Manual, where a change is recommended in the sensitivity of the UPS and making the change, it did not improve the fact that the UPS trips totally when switching from an Inverter supply to the Normal Power supply. Sometimes, it makes one wish not to go for costly known products that do not perform, and rather stick to local/unknown brands that are more reliable.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:27 AM

0 Likes
1
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:27 AM

Hi ruva,

The issue you have described is what is typically observed from a groundloop existing in your system. I would suggest disconnecting all datalines, which may be connected to any device receiving power from the BR1100CI and attempt a pull plug test to help confirm this. Groundloops often exist over Datalines connected between two devices which are receiving power from two separate electrical sources, that do not share a ground reference.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:27 AM

0 Likes
0
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:54 PM . Last Modified: ‎2024-03-21 01:27 AM

I have a little bit different types problem ,charging voltage is not proper,its showing 24.57

What's matter

  • Tags:
  • charging
  • low
Reply

Link copied. Please paste this link to share this article on your social media post.

wstar123
Ensign wstar123
Ensign

Posted: ‎2024-07-04 05:13 AM

In response to BillP
0 Likes
0
2044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-04 05:13 AM

Can you please continue this discussion in my thread here because I am experiencing a similar issue:

 

https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/UPS-seemingly-turn-off-during-square-w...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore