Back UPS shuts down but Replace Battery light not on
Select a Country
  • Back UPS shuts down but Replace Battery light not on
BillP Leader
2150
150
83
Posted: ‎2021-06-29 09:14 PM . Last Modified: ‎2024-03-20 04:24 AM
1311
I have a 10 year old Back UPS RS 800 with a 2 year old battery. The unit is shutting down regularly, without alarm and the Replace Battery light is not on. I'm trying to figure out if I can simply replace the battery or if I need a new unit.
My syslog (xubuntu 12.04) sees proper shutdown:
Nov 13 09:55:14 imagine apcupsd[2720]: Power failure.
Nov 13 09:55:14 imagine apcupsd[2720]: Battery power exhausted.
Nov 13 09:55:14 imagine apcupsd[2720]: Initiating system shutdown!
Nov 13 09:55:14 imagine apcupsd[2720]: User logins prohibited
And the self test passes, but the battery reports 0% (see below). Do I have a faulty unit? Are there any other tests I can/should perform?
Thanks!
=Fen
# apctest
2013-11-13 10:22:49 apctest 3.14.10 (13 September 2011) debian
Checking configuration ...
Attached to driver: usb
sharenet.type = Network & ShareUPS Disabled
cable.type = USB Cable
mode.type = USB UPS Driver
Setting up the port ...
Doing prep_device() ...
You are using a USB cable type, so I'm entering USB test mode
Hello, this is the apcupsd Cable Test program.
This part of apctest is for testing USB UPSes.
Getting UPS capabilities...SUCCESS
Please select the function you want to perform.
2)  Perform self-test
Select function number: 2
This test instructs the UPS to perform a self-test
operation and reports the result when the test completes.
Clearing previous self test result...CLEARED
Initiating self test...INITIATED
Waiting for test to complete...COMPLETED
Result of last self test: PASSED
10) Perform battery calibration
Select function number: 10
This test instructs the UPS to perform a battery calibration
operation and reports the result when the process completes.
The battery level must be at 100% and the load must be at least
10% to begin this test.
Battery level 0% is insufficient to run test.
4)  View/Change battery date
Select function number: 4
Current battery date: 05/13/2011
5)  View manufacturing date
Select function number: 5
Manufacturing date: 08/02/2003
  • back-ups
  • failure
  • question
  • replacement
  • shutdown
Couple of things to check / try:
1. Make sure the Anderson or faston connections to the battery are good and tight. If its weak it could drop loads unexpectedly.
2. Try to brain dead the ups (to reset its internals ) by pulling the plug, let it run on battery til it dies, unplug the battery to finish kill of all power sources, reconnect the battery and plug the ups in. Wait 6 to 8 hrs for the battery to charge then power it on and let it do a self test.
BillP Leader
Leader
I suggest taking advantage of the APC Trade-UPS program (if available in your region) to replace the unit. APC Trade-UPS