Hello all,
we have an "Back-UPS XS 700U" and using the PowerChute Business Edition we are facing some issues with Version 9.5 and 10.
1. If we configure the System to "Shutdown" it Shutsdown the System (Host-PC) but all other Devices connected to UPS are still running from the Battery until the UPS Battery is empty. Why is the UPS itself not Powering off after a "power-outage" and the Computer got Shutdown ? Is there any Setting to power-off the UPS after "x" time?
2. The Values like "Battery Charge" or "Input Voltage" "Internal Temperature" in the PowerChute Business Edition are all wrong.
Hopefully someone can help.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:15 AM . Last Modified: 2024-03-26 03:32 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:15 AM . Last Modified: 2024-03-26 03:32 AM
Hello Bill,
we have now Installed the correct Software, the values are now showing up correct.
But can you maybe give an Answer to Question1:
1. If we configure the System to "Shutdown" it Shutsdown the System (Host-PC) but all other Devices connected to UPS are still running from the Battery until the UPS Battery is empty. Why is the UPS itself not Powering off after a "power-outage" and the Computer got Shutdown ? Is there any Setting to power-off the UPS after "x" time?
I dont find any setting on the PowerChute Personal Edition that allows to Shutdown the UPS itself after PC got Shutdown.
Is this possible with the UPS we are currently using?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:15 AM . Last Modified: 2024-03-26 03:32 AM
Hi,
PowerChute Business Edition is not compatible with a Back-UPS. Back-UPS are compatible with PowerChute Personal Edition. Here is a link to PCPE. https://www.apc.com/shop/us/en/products/PowerChute-Personal-Edition-v3-1/P-SFPCPE31
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:15 AM . Last Modified: 2024-03-26 03:32 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:15 AM . Last Modified: 2024-03-26 03:32 AM
Hello Bill,
we have now Installed the correct Software, the values are now showing up correct.
But can you maybe give an Answer to Question1:
1. If we configure the System to "Shutdown" it Shutsdown the System (Host-PC) but all other Devices connected to UPS are still running from the Battery until the UPS Battery is empty. Why is the UPS itself not Powering off after a "power-outage" and the Computer got Shutdown ? Is there any Setting to power-off the UPS after "x" time?
I dont find any setting on the PowerChute Personal Edition that allows to Shutdown the UPS itself after PC got Shutdown.
Is this possible with the UPS we are currently using?